i have and here they are for your perusalLets get this straight, has anyone checked the MI's? I have. This boiler does not have a seperate plate heat exchanger. Its heat exchangers HTG + DHW are both located above an atmospheric burner. So when it calls for HTG it also heats the DHW side regardless of DHW demand. So if the DHW side become empty through evaporation because the water is turned off then the consequences could cause damage.
Agree with everyone if it had a seperate plate heat exchanger heated from the main HTG heat exchanger through a diverter valve. Which is the normal for all your Vaillants, Worchesters ect, but not for an old ferrolli Modena.
Also agree that the overheat would probably protect it. but would not rely on it as thats your last line of safety device.
http://www.ferroli.co.uk/wp-content/uploads/brochures/archives/Ferroli F30 B Manual.pdf