Hi all

I had a complete new CH system installed a few months back. I did some research, got multiple quotes, went with a guy with a few good references and checked he was Gas safe registered. He did work very fast though. Perhaps too fast.

It runs 9 radiators from a Greenstar 38 Cdi combi. It's a two storey end terrace house, with about 120 square metres of floor space. The carcass is 22mm copper, with 15mm branches to compact Stelrad radiators. The boiler is upstairs at the back of the house. Another plumber already told me the boiler is too big for this house and so inefficient - I did ask for good water heating power, so maybe that's why he chose that one.

Questions:
1. From installation I thought the rads are small, but the plumber told me that's because they are compact. Anyway, sure enough, it takes about 45-60 minutes per degree of room temp rise in the two living rooms, from when the radiators are really hot on a night, when outside is below about 7 degrees, and this is with the boiler at maximum CH heat setting. I think this is unacceptably slow, as if the heating comes on when the room is 16 degrees, takes 15 minutes to heat the rads, then I'm looking at 5 hours to get to 21 degrees, which is mad (and bedtime). I have checked this with an independent thermometer and it agrees with the thermostat on the rate of heating up the room. Needless to say, we're quite chilly with our brand new system.

The plumber is arguing that he's never had a problem with his BTU calculator and wants us to pay for the bigger radiators we need. I don't care about BTU calcs, as every house is unique and they are only a guide. I want to be sure this is an under-powered set of rads, based on how long it takes to heat up, before putting my foot down on who pays. Underpowered?

2. THE BIGGER QUESTION
With the above and other teething issues, it got me thinking to take a look at the piping. Now I realise that rather than take the flow and return to the front of the house upstairs, for the front and middle bedrooms (which are the lion's share of the upstairs floor space), he has instead taken a long two-pipe branch from the flow and return in the study at the back of house, where the boiler is, all the way to the farthest front room (8-10 metre), and also teed off this for the middle room. So two pipes emerge from study and run 8-10 metres along corridor into the master bedroom, one pipe into one end of a rad and one into the other. Near their beginning, outside the study, a tee is taken from each pipe to go 2-3 metres into and out of the middle bedroom's radiator. The pipework starts as 22mm and reduces to 15mm about 1metre from each radiator.

Is this just lazy but no great issue (the rads do heat up). I do have an attic conversion above the front bedroom, and the plumber knows I want to put a rad in there one day, but that means teeing off what is already an 8 metre branch.

3. The system used to creak terribly and woke us up in morning and kept us awake until fully cooled down at night. It's clearly the pipes touching joists and boards. We did manage to get the plumber back, grumbling somewhat that we're fussy, to put felting in the worst places. He said he's never had to put felt around joist notches for anyone before, but I find that odd, having read how common it is. Am I fussy or is felting standard? (better still, he could have cut floorboards so his pipes aren't touching them where they emerge). It still creaks a lot downstairs.

4. I don't know much about heating systems (obvious huh?). However, does the above indicate I should get a different plumber out to check the system?
If so, what are my rights? I paid about £7k for the system (No VAT, as he's not VAT registered).

Many thanks for any input.
Alex
 
just somthing to throw into the mix. how many other gas appliances do you have in the house ? and did the other plumber who came round to have a look at your issues did he check the gas pipe size to the boiler ? have him check the boiler commisioning report.
but please for your own safety dont touch the boiler yourself.
 
just somthing to throw into the mix. how many other gas appliances do you have in the house ? and did the other plumber who came round to have a look at your issues did he check the gas pipe size to the boiler ? have him check the boiler commisioning report.
but please for your own safety dont touch the boiler yourself.

Thanks 1967skyblue



Two small gas fires downstairs. But the boiler is run off a separate, dedicated new main supply from the meter. Not had someone come and look on site yet. What should I be getting them to look for? Does system sound in need of checking over for general competence?
 
Another plumber already told me the boiler is too big for this house and so inefficient
Is the boiler continually turning on and off while the house is heating up?

Did the installer measure the incoming cold water flow rate and dynamic pressure before recommending a 38kW boiler?
 
QUOTE: The plumber is arguing that he's never had a problem with his BTU calculator and wants us to pay for the bigger radiators we need. I don't care about BTU calcs, as every house is unique and they are only a guide. I want to be sure this is an under-powered set of rads, based on how long it takes to heat up, before putting my foot down on who pays. Underpowered?

BTU calculator? Hope he calculated the whole house heat loss method as well?
 
Best plan is for you to measure the rooms width/length and height, post this on here with each room named and state no of windows, outside walls also.

Then measure the rad size installed in the room - and state wether its a single,
double, or 3x with fins or not - type radiator.

We (on here ) can work out what rads we would have supplied.

centralheatking
 
  • Like
Reactions: 1 person
Simple ask him to provide the design & heatloss calculations he used to size & then select the rads, as you believe they are undersized & this is the cause of the system (product) you have paid a lot of money for not working correctly, give him a few days to provide these & the chance to correct the problem otherwise you will have to go see trading standards & the court. You may need to get another engineer in to prepare a report on the installation to back up your claim. (see CIPHE)

As others have said it could also be the boiler heating output is to large for the load but most likely it is the rad's.
 
As others have said it could also be the boiler heating output is to large for the load but most likely it is the rad's.
The OP has a boiler which modulates between 9.4kW and 30kW. He has 9 rads, which at, say, 1.5kW each is 13.5kW total load. Even if they were 2kw, which is doubtful, that would still be only 18kW. So whichever way you look at it the boiler is oversized for the heating load.

There's a good chance that the flow water temperature rises to 75, or whatever is set, but the return temperature keeps on rising, meaning the boiler then cuts out, waits and then restarts. So the mean water temperature is well below the required value, which means the rads are not giving off the correct amount of heat.

The OP should use Whole House Boiler Size Calculator to find out the heating requirement and Stelrad Elite Catalogue, first table to estimate the output of his radiators.
 
  • Like
Reactions: 3 people
The OP has a boiler which modulates between 9.4kW and 30kW. He has 9 rads, which at, say, 1.5kW each is 13.5kW total load. Even if they were 2kw, which is doubtful, that would still be only 18kW. So whichever way you look at it the boiler is oversized for the heating load.

There's a good chance that the flow water temperature rises to 75, or whatever is set, but the return temperature keeps on rising, meaning the boiler then cuts out, waits and then restarts. So the mean water temperature is well below the required value, which means the rads are not giving off the correct amount of heat.

The OP should use Whole House Boiler Size Calculator to find out the heating requirement and Stelrad Elite Catalogue, first table to estimate the output of his radiators.
I agree totally with you on the technical bits above & asking the installer for his design criteria (or lack off) would provide proof of poor design practice be it the rads or boiler.
Is it not possible with these to down rate or limit the heating output to say 15-18kW, as with the Vaillants ?

Not so sure the OP should have to do any calculations to confirm one way or the other, there are to many variables, all they should have to point out is that it has been cold & the new heating was not heating the house to a normal standard.
 
  • Like
Reactions: 1 person
30 kw on 9 rads should mean the place is steaming hot - I run my place with a 30kw boiler - 5 bedrooms, 3 bathrooms and hot water cylinder and never have to go past 3/4 heat - thats 16 rads and none are small. r
The OP has a boiler which modulates between 9.4kW and 30kW. He has 9 rads, which at, say, 1.5kW each is 13.5kW total load. Even if they were 2kw, which is doubtful, that would still be only 18kW. So whichever way you look at it the boiler is oversized for the heating load.

There's a good chance that the flow water temperature rises to 75, or whatever is set, but the return temperature keeps on rising, meaning the boiler then cuts out, waits and then restarts. So the mean water temperature is well below the required value, which means the rads are not giving off the correct amount of heat.

The OP should use Whole House Boiler Size Calculator to find out the heating requirement and Stelrad Elite Catalogue, first table to estimate the output of his radiators.
 
  • Like
Reactions: 1 person
Is it not possible with these to down rate or limit the heating output to say 15-18kW, as with the Vaillants?
According to the Installation Manual, the Max output can be adjusted but, unhelpfully, they don't tell you how to do it.

Not so sure the OP should have to do any calculations to confirm one way or the other
It won't do any harm to have some figures to back you up. "I feel cold; and this is why!"
 
  • Like
Reactions: 1 person
I have said it before but here goes COMBI'S ARE EXEMPT FROM WHOLE HOUSE HEAT CALCS!.......
due to many reasons but the main one is that their outputs are based upon hot water production, obviously this should be matched to incoming mains water pressure and gas runs from a responsible installer but often are not!

To get round this good manufactures get round this by allowing range rating.

Worcester bosch get around this on the junior and Si with a code plug that down rates from 24kw to 12 kw, the CDi can be adjusted from 30kw to around 9 kw on 38 and 42 CDi and 30 kw to 7 kw on 29 and 34 Cdi (this can only be accessed via installer menus, I am not posting how as the menu contains all stuff that should not be touched unless you are trained by WB, pump maps, turbine delays, and much more!

the 38 Cdi is actually 40 kw on DHW NOT 38 marketing bluff as not to pull sales from 42 cdi

i actually look after some trendy apartments that have 42cdi's and 2 rads and a towel rail! 42 kw for hot water due to silly sized baths!
 
  • Like
Reactions: 4 people
go on the worcester course and you will get taught how to range rate the cdi. Or phone the tech helpline and get talked through it.
 
I have said it before but here goes COMBI'S ARE EXEMPT FROM WHOLE HOUSE HEAT CALCS!.......
due to many reasons but the main one is that their outputs are based upon hot water production, obviously this should be matched to incoming mains water pressure and gas runs from a responsible installer but often are not!
I agree that Hot Water production is the overriding factor when sizing a combi boiler, but the specifier has to take the Central heating requirement into account. If he doesn't you can get the situation where the minimum CH output is above the CH requirement of the house. For example a house with an 8kW heating requirement which has a Vaillant 837 or 937 installed (12-28kW CH output)
 
  • Like
Reactions: 2 people
possibly the ops best course of action may be to get wb in to see whats wrong if he calls it in as a boiler fault they will then tell him if its an installation fault they may charge him if theres no boiler fault but then he will have an idea of whats wrong and can claim against the installer if there remedial work needed
the pipework sounds ok in that theres 2 pipes going every where and in 22 to within one meter of every rad sounds over kill
 
To add to doitmyself post above the problem is not always the down rating or modulation of these lager boilers the one thing that the engineers changes can't change (as far as I know) is the CPU's electric control routines which run the start-ups firings, modulations & anti cycling etc all of which remain pre-set for the largest outputs & can still effect the boilers performance even when down rated.
 
I agree that Hot Water production is the overriding factor when sizing a combi boiler, but the specifier has to take the Central heating requirement into account. If he doesn't you can get the situation where the minimum CH output is above the CH requirement of the house. For example a house with an 8kW heating requirement which has a Vaillant 837 or 937 installed (12-28kW CH output)

The technical reason are turn down ratios.....but even the 42 CDI's i look after don't have this problem, with 3 rads if set up right, min output, anti cycle delay adjusted from standard 3 mins, for reference the Cdi does not have a return sensor, just flow with is mapped via PCB software to keep flow temp to within 5 dregs of set point on boiler stat, this can also be adjusted in menus but not if you don't know what you are doing, any GSR can fit a boiler ( commissioning and maintenance is altogether a much tougher job)
 
  • Like
Reactions: 1 person
To add to doitmyself post above the problem is not always the down rating or modulation of these lager boilers the one thing that the engineers changes can't change (as far as I know) is the CPU's electric control routines which run the start-ups firings, modulations & anti cycling etc all of which remain pre-set for the largest outputs & can still effect the boilers performance even when down rated.

Incorrect Chris on WB anyhow, I was typing the above whilst you replied
 

Official Sponsors of Plumbers Talk