Hi all.

I've been asked to quote against another installer on a house that has a pretty old system.

The house is very old, and plush internally. Infact it was built in the 1500's.

Guess the heating system is older than me. The client has always been on oil, but has recently taken an opportunity to have mains gas installed.

I've been asked to quote against a couple of others who have quoted to install two cascaded WB 30CDI's, with the Worcester Bosch low loss header.

I take a bit of an issue with this, as the WB LLH isn't designed for a vented system. The way I see it, you could remove the air vent in the top and run it to the open vent but that smacks of a bodge to me (badly).

I'm a bit loathe to seal the system but I've only ever installed LLH's on sealed systems. I don't see why I couldn't have a LLH made up with a proper sized vent on the top for expansion.

Has anyone been in a similar situation? Maybe I should just quote as the others have and seal the system.

I have read on here in the past about people using plate heat exchangers to seperate the boiler from the old pipe work, but have no experience of doing this myself other than repairing a couple of swimming pool boilers in the past!!

It's a nice local job and I want the gig but not if it's going to be agro down the line!
 

Attachments

  • Capture.jpg
    Capture.jpg
    88.1 KB · Views: 162
Ill ask ali tomorrow danny.

i know we have done atleast one open vented low loss header but that system was huge.
However that was a heat exchanger to the low loss header. Boiler room was 300 yards away.

In my view sealing the system is a bad idea, from the looks of it that place is listed?

give wb a ring and queery them, if that fails look at having one made to your spec.
 
Yeah, it must be listed. It's totally immaculate inside too.

I've called WB and they say their LLH is designed only for a sealed system. I will have to either make one myself which I have no problem doing but will cost me more in pipe and fittings than you can buy one for.

Nice to hear from you BTW mate. How's things?
 
I suppose your other little issue will be how dirty the system is,
I'm betting the oil boiler was a low resistance design so it didn't matter a damn.
a modern boiler hex wont cope?
a spirocross could be an option ?
Give them a look up.
Or you could use a bowmen style heat exchanger between the sealed and open vented systems.

I've seen your quotes and they are ace, i would list why you would not seal the system and the risks.
It might shoot down your rival.

It isn't north pole energy you're quoting against is it?!

Im great, i'm a little faster now too!

i still haven't fixed the leak in the van! I need to asap, every morning its misted up oh so badly 🙂

yourself?
 
Yeah the system will be black as the night.

I've been sent the other two quotes, but just a snip of their wording, no logo's or prices! Their quotes are very thin, with no proper details.

I was thinking about fitting a Spirocross, but then thought it may be simpler and cheaper to stick a couple of ceonventional 28mm TF1's (or similar) on the returns from the headers to the boilers.

I have no idea who it is I'm pricing against. I bumped into the customer and he asked for my number. I had done work for him a few years back but he had lost my number. He's keen for a price asap as he want to award the job to who ever wins and get it booked in. Which is understandable as his existing oil boiler is knackered.
 
Oh and I'm good thanks.

Will it take much to get the leak sorted, did you find out exactly where it's getting in? Sorry about that mate!! Other than that has it been behaving?
 
The reason i suggested a spirocross was that it has a beefy mesh inside.
maybe put an inline strainer before the tf1?

Oh i haven't pulled it apart yet to see, im sure a bit of mastic will solve it!

behaving? Hmmm
i had fuel trouble like you did 😛

in the end it turned out to be inside the body some of the wiring to the low pressure fuel pump was damaged, every so often to would break and then make after some playing around.

had that replaced and its been fine since then!
Could have been the same story when you had it?
 
Jesus, I'm sorry Billy. Why didn't you call me? I never did get round to sending you the receipt for the work I did to the van...but it had a grand's worth of repairs, and a £380 service before I sold it to you, so I genuinely thought it was straight.

Did it set you back much £££.

Oh and I haven't done the heat calc for the property. I've questioned it, but he's had it worked out by a few blokes and it's all coming in at least 55KW. I just have so much on at the moment, that I need to get the quote out and then question boiler size... It's a pretty large property, and as Billy says....the heat loss is a disaster. Getting insulation in a house that age is going not a small undertaking.

Don't know about anyone else on the forum but I've been mental busy. Only had a couple of days off in the past 8 weeks. Worked a 14.5 hour day on Saturday, 8pm yesterday. Just can't catch my breath!
 
Danny i brought the motor knowing the history!!
do not feel bad!
No it didn't, just an oil boiler service and changing a few taps for the guy 🙂

As far as I'm concerned its a great van and suits me for what i need 🙂

although if you get a chance i wouldn't mind that paperwork at some point? When you have time ofcourse!

If you need a hand at any point just shout Danny, i'll be yours for the fuel money and experience as
i still view myself as an apprentice, i'm nowhere near as fast or experienced as i need to be yet 🙂
 
I'd be looking at Intergas for an old system. The 22mm waterways are much less likely to give problems with sludge.
 
Probably good advice Mike, but I've been asked to quote 'like for like' so my hands are tied on that front. Apparently I'm the 4th bloke to visit, and the others all suggested a WB. To be fair, I fit a lot of WB and trust the brand.
 
Mike makes an extremely good point tbh.
intergas or separate the two systems?

At the end of the day, would you prefer to price the job to do it right first time and have no issues but risk not getting the job?

or do the job to the other peoples spec, beat them on pricing and have issues down the line?

i have no idea the waterway size on a cdi system boiler but I'm guessing 12mm or smaller?
can someone clarify?
 
Yeah, I don't want the job if it's going to be a ball ache down the line. I know the system is going to be full of crud.

It's worth considering, I'm under pressure to get the quote out. Got a load of bathrooms to quote for too, but I'd much rather win this work and forgo the bathrooms as this will be more interesting for me. So I'm keen to win it.
 
I did the intergas 5 year warranty thingy me bob course. If I'm free tomorrow i will ring up and see if that could be used with you registering the boiler still. Leaving you free with that option.

To separate the systems you need a high water content heat exchanger that can transfer 60kw of heat.
or a pair of 30 kw ones.

then you will need an additional pump. Four in total.

The two boiler pumps to run their own circuit to the low loss head
one from the low loss header to the heat exchanger.
another for the main system.
with that option you could use the WB llh as that would be sealed.



you could bin the low loss header completely.
have each boiler run its own heat exchanger
have both heat exchangers in series for the house side.
 
Last edited:
Like I said, I don't have any real experience of using plate heat ex's to protect the new plant, but surely if the system water is bad, it can damage the new heat ex? How much are they?! 🙂
 
No worries, I'm going to give the customer a call tomorrow and have a chat with Intergas.

Pretty sure I'm going to quote to fit the two 30cdi's and make my own LLH. Keep the system open vented, and fit a pair of 28mm filters on both the returns. That keeps it fairly simple.

If anyone else cares to comment, I'm always open to other opinions.
 
Hi Danny hope you and the family are keeping well, nice to see you back on the forum.

I cant offer advice on the specification for the boiler but one piece of advice:-

When a customer has already had 3/4 quotes already and need a price asap I normally find they have already made up their mind of an installer, they are still trying to convince themselves they have made the right choice. Or the job will never happen !!

Try not to waste too much time on the estimate unless you think it will help your knowledge in the future.


Kev.
 
Two ideal logic plus 30kw on a cascade with LLH open vent is simple and works a treat. Only problem u got is the listed status. Do they have consent for flues and plant!!? Magnanaclean 28mm on return from LLH. Boilers need to be co current connections when in cascade. Boiler 1 gets flow first and ret seconds and boiler two gets flow second and return first.
 
Hi Kev, good to be back on here.

Family are all well thanks, adding one more to the clan as of February.

I hope you and your family are well too mate. I still haven't got round to fitting that panel I had off you!! Ha. It's in the mother in the mother in laws garage waiting until I have a quiet week. Oh and can find a cheap pump station!

I'm not going to waste too much time with the quote, but I do want the job over some of the bathrooms I'm quoting for. I'd rather earn a little less and not have the head ache of organising all the other trades if I'm totally honest!
 
Two ideal logic plus 30kw on a cascade with LLH open vent is simple and works a treat. Only problem u got is the listed status. Do they have consent for flues and plant!!? Magnanaclean 28mm on return from LLH. Boilers need to be co current connections when in cascade. Boiler 1 gets flow first and ret seconds and boiler two gets flow second and return first.

Thanks for that.

Can you explain why you have to configure the f&r's like that? To maintain an equal flow rate I'm expecting.

I'm also going to quote to fit a sequencer though looking at the other quotes, they haven't. I've installed one before and it's worked well. I used the Warm World model. In fairness it broke after two years (a relay went) but the new one has been in a couple of years now and is all good.
 
Thanks for that.

Can you explain why you have to configure the f&r's like that? To maintain an equal flow rate I'm expecting.

I'm also going to quote to fit a sequencer though looking at the other quotes, they haven't. I've installed one before and it's worked well. I used the Warm World model. In fairness it broke after two years (a relay went) but the new one has been in a couple of years now and is all good.

It's what ideal tell you to do when cascading them, assume its to maintain even flow. U need only connect the pump for the boilers to the boilers and the system pumps to controllers
 
Danny I may be able to help you there !!

I am removing a SoSolar system this week
http://www.ukplumbersforums.co.uk/renewable-energy/60513-rusting-solar-expansion-vessel.html

I was going to butcher the system whilst removing for ease, but if you want it I will take care.

The pump station will need a thorough flush, the Pressure gauge I presume needs a little clean of the hole.

There will be a cylinder sensor and control panel.

Please let me know asap as it is coming out on Thursday, the customer has had enough of a poorly designed/installed system.

Kev
 
Mate that would be much appreciated and of course I'd be happy to pay you. Let me know what you want for it mate. PM me if you want. The mother in law will be pleased as it can stay in her garage until the spring!! LOL.
 
Well thanks very much Kev. Please put my name to it. Looks like I'll be driving out to your place again! I will come loaded with a a few crates of wife beater!!
 
Just bumping this thread as I won the job and am speccing the install.

I was going to use two 15/60's as the shunt pumps. I was on ebay, looking for something else, and came across a UPS2 25-40. Which looks suspiciously like a pump from an underfloor heating manifold. It's A rated, and a good price. I called Grundfos who told me it isn't a UK pump so don't know where they got them from. It will probably do the job but they suggested I go through a merchants for warranty reasons.

I like the idea of using a pump with a bigger bore. I think I may be confused though as Grundfos said this pump doesn't have a bigger bore. Surely being a 25/40 the bore is 25mm as opposed to 15?

Anyone have any comments to make on this?
 
this is a really interesting thread. i don't work on anything over 4 beds in my area. does anybody have any link to info i can read about the systems /design your discussing.

1 quick question is it ok to cascade boilers on domestic ticket as long as it its below75 kw or is this strictly in the realms of commercial.

thanks all
 
Hi Jules. It's fine to cascade boilers up to your limit. I've cascaded oil boilers to over 80KW in the past, but that was working alongside my dad who was a commercial fitter for years. Oil didn't even have a commercial qualification until about a year or so ago. Croppie was one of if not the first one in the country to qualify for it.

By the way the limit with gas is 70KW not 75. Here's a snip lifted from Kirk a couple of years back.

~ domestic is up to 70kw appliance, or pipework up to 35mm as long as it contains a total installation volume of less than 0.035m3, a U16 meter can be used depending on overall volume not exceeding 0.035m3
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "New install on an old system." which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
Dannypipe,
Last reply from
Dannypipe,
Replies
83
Views
1,934
Back
Top