Turn partial load off of auto and rate it for the smallest zone?
I did do this at one stage, but found the system was very slow to heat up with both upstairs and downstairs calling for heat.
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Turn partial load off of auto and rate it for the smallest zone?
but am still curious as to how one would setup a system from scratch to cater for multiple zones (without a low loss header).
I'm having difficulty with accepting this.the data you gave appear to indicate that you cannot drop the boiler flow less than 0.45 ls so this is the max and min flow rolled into in, in other words the boiler manufacturer doesn't want any reduction in boiler flow at any time.
The latest version of the PCB is supposed to cure this problem; but the OP already knows this and has the new board installed. We don't know if it has had any effect.The problem with Vaillant 438 is even if you range rate the boiler down to 12 kw it will still fire at 60percent of its max ( 60% of 38kw) and then ramp up!!! Yes UP before it come down to 12kw.
The latest version of the PCB is supposed to cure this problem; but the OP already knows this and has the new board installed. We don't know if it has had any effect.
You should have fitted a MAGNA1 25-60 or 80 not the UPS
Set partial load to 12kw