If you have the Domestic Heating Design Guide it is section 13.8 (well it is in my old one)
flow rate = H / (TD x SH) = kg/s where
H = heat output in watts (50kW = 50,000 watts)
TD = temperature difference between flow & return in deg C (either 11 old or 20 new systems/boilers)
SH = specific heat of water in J/kg (which is 4186)

So flow rate = 50000 / (20 x 4186) = 50000 / 83720 = 0.5972 kg/s round it up to 0.6 kg/s
Using Tables 13.1a & b look down the column's of figures until you see >0.6 above the 0.5 m/s Velocity line that works it way across the table/page, in this case it appears in the first column on table 13.1b which is 42mm pipe size but it is only just, it might be better to use the next size up i.e 54mm in which case the velocity would drop to around 0.3 m/s.
So rule of thumb boilers up to 50kW can be connected to a 54mm copper or larger L.L.Header if using a delta T of 20deg C.
The pipe work connections should be arranged so that all the flows are at one end & all the return are at the other with a reasonable section of clear pipe between (say 150mm or 5 x inlet pipe dia minimum)
The F&R to boiler/s (or any draw off circuit) could be sized in the same way as above but normal velocity for domestic systems is </=1.0 m/s. Or use the quick pipe sizer 13.2 (28mm can carry upto 40,000 to little & 35mm upto 62,000) so 35mm it is.
Better to arrange header so it is in the vertical (air & dirt separation) & make sure it has an AAV on top end & drain off on bottom.
Anyone got any thing to add (have I got it right ?)
 
Last edited:
If you have the Domestic Heating Design Guide it is section 13.8 (well it is in my old one)
flow rate = H / (TD x SH) = kg/s where
H = heat output in watts (50kW = 50,000 watts)
TD = temperature difference between flow & return in deg C (either 11 old or 20 new systems/boilers)
SH = specific heat of water in J/kg (which is 4186)

So flow rate = 50000 / (20 x 4186) = 50000 / 83720 = 0.5972 kg/s round it up to 0.6 kg/s
Using Tables 13.1a & b look down the column's of figures until you see >0.6 above the 0.5 m/s Velocity line that works it way across the table/page, in this case it appears in the first column on table 13.1b which is 42mm pipe size but it is only just, it might be better to use the next size up i.e 54mm in which case the velocity would drop to around 0.3 m/s.
So rule of thumb boilers up to 50kW can be connected to a 54mm copper L.L.header if using a delta T of 20deg C.
The pipe work connections should be arranged so that all the flows are at one end & all the return are at the other with a reasonable section of clear pipe between (say 150mm or 5 x inlet pipe dia minimum)
The F&R to boiler/s could be sized in the same way as about but normal velocity for domestic systems is <1.0 m/s or use the quick pipe sizer 13.2 (28mm can carry upto 40,000 to little & 35mm upto 62,000) so 35mm it is.
Better to arrange header so it is in the vertical (air & dirt separation) & make sure it has an AAV on top end & drain off on bottom.
Anyone got any thing to add (have I got it right ?)



You tell us you're the instructor, sounded impressive
 
Looks good to me, Chris and seems to tally up with the sizing and rating of the LLH manufacturers. Easier to understand than the original calculation suggestion I posted back in 2012.

This is is at bit of a thread resurrection.
 
lvh.jpg
 

Thats not really a header. Its more like a spirocross air and dirt seperator.
You can make your own up just the same.
Design it at around 2 litres/kw with a flow rate of 0.1m/s or less. That allows for the muck to settle and stratification to take place.
You can make a better one yourself anyway. Its easy if you know how.
 
Last edited by a moderator:
I usually make my own. As a rule of thumb I usually make the header 2-3 sizes bigger than the biggest primary pipework size and this always works for me. For example on a 45kw loads I used 35mm primarys, and then made one with 54mm tube. Flow and returns have to be a minimum of 800 apart.

This is a rule of thumb method iv used and obviously not the technical way of doing it, but they always work well for me. Always better going on the larger size.
 
Thats not really a header. Its more like a spirocross air and dirt seperator.
You can make your own up just the same.
Design it at around 2 litres/kw with a flow rate of 0.1m/s or less. That allows for the muck to settle and stratification to take place.
You can make a better one yourself anyway. Its easy if you know how.


Tamz,

If I turn that drawing on its side will you be happy will it look like a LLH then, bloody Scots, :90: never happy "Independence Day" hey Tamz, :furious3:what will your currency be then "Groats"
 
We need to build Low Loss Header for chiller-fancoil piping system, however we do not have enough information. I have some questions about designing L.L.P?

  1. Are the secondary connection and primary connections are exactly opposite?
  2. Some manufacturers add a baffle plate inside the LLP, does it recommend?
  3. We design the diameter of LLP, with 2 ft/s velocity, is it correct?
  4. Is it correct to suppose the distance between the inlet and outlet connections equal to 4*diameter of connection?
 
What's consultant spesified? Never go opposite unless baffled
 
Last edited by a moderator:
Don't make it too big you want turbulent not laminar flows across the ports. So it mixes

What's the heat load ?
 
Last edited by a moderator:
Chiller system?

you're playing by a different set of rules to us then if i remember rightly.

get it designed imho
 
We need to build Low Loss Header for chiller-fancoil piping system, however we do not have enough information. I have some questions about designing L.L.P?

  1. Are the secondary connection and primary connections are exactly opposite?
  2. Some manufacturers add a baffle plate inside the LLP, does it recommend?
  3. We design the diameter of LLP, with 2 ft/s velocity, is it correct?
  4. Is it correct to suppose the distance between the inlet and outlet connections equal to 4*diameter of connection?


Are we on chilled water here or heating, LL headers are not rocket science they can't be it's plumbing :smilewinkgrin:
 
The chap's from Iran and doesn't strike me as a spammer so there could be some translation losses guys.
 
Emi, I will weld up the LL header, fly it down there and you fit it, we will need about 10 refuel stops from your hoose in a single engine Piper
 
I'm making sarnies hope u like tea! Loaded up batton berg and space invaders.


Take mi 30 mins to make up the header, take us 4 weeks to fly it down there, if we get stopped in customs anywhere with the header
you can do the explaining what is for in broad jordie, they won't have a clue. Wi I mun
 
Last edited by a moderator:

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Calculate size of low Loss Header" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
gary j,
Last reply from
missplumb,
Replies
69
Views
44,913
Back
Top