Tamz,
Was that a good guess Tamz, your formula was near enough.
Was that a good guess Tamz, your formula was near enough.
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
If you have the Domestic Heating Design Guide it is section 13.8 (well it is in my old one)
flow rate = H / (TD x SH) = kg/s where
H = heat output in watts (50kW = 50,000 watts)
TD = temperature difference between flow & return in deg C (either 11 old or 20 new systems/boilers)
SH = specific heat of water in J/kg (which is 4186)
So flow rate = 50000 / (20 x 4186) = 50000 / 83720 = 0.5972 kg/s round it up to 0.6 kg/s
Using Tables 13.1a & b look down the column's of figures until you see >0.6 above the 0.5 m/s Velocity line that works it way across the table/page, in this case it appears in the first column on table 13.1b which is 42mm pipe size but it is only just, it might be better to use the next size up i.e 54mm in which case the velocity would drop to around 0.3 m/s.
So rule of thumb boilers up to 50kW can be connected to a 54mm copper L.L.header if using a delta T of 20deg C.
The pipe work connections should be arranged so that all the flows are at one end & all the return are at the other with a reasonable section of clear pipe between (say 150mm or 5 x inlet pipe dia minimum)
The F&R to boiler/s could be sized in the same way as about but normal velocity for domestic systems is <1.0 m/s or use the quick pipe sizer 13.2 (28mm can carry upto 40,000 to little & 35mm upto 62,000) so 35mm it is.
Better to arrange header so it is in the vertical (air & dirt separation) & make sure it has an AAV on top end & drain off on bottom.
Anyone got any thing to add (have I got it right ?)
Tamz,
Was that a good guess Tamz, your formula was near enough.
Doesn't mean it or I am right does it, looking for your input. Which might be useful to us all.You tell us you're the instructor, sounded impressive
Your just the bl**dy same as the rest of my students, attention span of a goldfish. LOLGoing so well and then i got bored towards the end lol!
Your just the bl**dy same as the rest of my students, attention span of a goldfish. LOL
Bit of 100mm box section plate top and bottom 😉 any one ?
In which case you were much much better than the normal ones which sit in front of me !I was a student of yours, mature one at that!
Thats not really a header. Its more like a spirocross air and dirt seperator.
You can make your own up just the same.
Design it at around 2 litres/kw with a flow rate of 0.1m/s or less. That allows for the muck to settle and stratification to take place.
You can make a better one yourself anyway. Its easy if you know how.
never happy "Independence Day" hey Tamz, :furious3:what will your currency be then "Groats"
We need to build Low Loss Header for chiller-fancoil piping system, however we do not have enough information. I have some questions about designing L.L.P?
- Are the secondary connection and primary connections are exactly opposite?
- Some manufacturers add a baffle plate inside the LLP, does it recommend?
- We design the diameter of LLP, with 2 ft/s velocity, is it correct?
- Is it correct to suppose the distance between the inlet and outlet connections equal to 4*diameter of connection?
The chap's from Iran and doesn't strike me as a spammer so there could be some translation losses guys.
The chap's from Iran and doesn't strike me as a spammer so there could be some translation losses guys.
You do at night!
I'm making sarnies hope u like tea! Loaded up batton berg and space invaders.
Reply to the thread, titled "Calculate size of low Loss Header" which is posted in UK Plumbers Forums on Plumbers Forums.
We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.