maybe a daft question? ...........

View the thread, titled "maybe a daft question? ..........." which is posted in UK Plumbers Forums on UK Plumbers Forums.

N

nysk2008

hi all,

so scenario is a standard boiler service only, no other appliances touched, just visual.

No full tt done as boiler tightness checked and 2mb drop, fail ID, obviously if a tt was done at lets say a u6 with no smell it would be a permissable drop.

now, what would you do?

just curious as its probs a bad question with an immediate answer but i;d like to know
 
Max allowance of 4mbar over 2mins with a u6 existing instal. unless the leaks in the pipework then its a fail.and theres no smell. Isolate all app and do test to make sure leak not on pipework.
 
Max allowance of 4mbar over 2mins with a u6 existing instal. unless the leaks in the pipework then its a fail.and theres no smell. Isolate all app and do test to make sure leak not on pipework.
thanks kris, but ive been taught gv passing ID but different tests would show a different classification, strange one mate appreciate your feedback
 
I didnt realise u ment the gas valve passing. I thought u done a tt and had 2mbar of drop. My mistke nysk
 
boiler isolated by stopcock, passing at p1, but my point is mate it wouldnt pass on a boiler tt but would on a normal tt, thats what I cant get my head around
 
If youve determined gas valve passing your right defo fail. Did u use water gauge or digital . I always use my fga but sometimes i do the test multiple times as the sensors give off wrong readings depending if i open valve to quick
 
If youve determined gas valve passing your right defo fail. Did u use water gauge or digital . I always use my fga but sometimes i do the test multiple times as the sensors give off wrong readings depending if i open valve to quick
i only ever use water mate on any sort off tt whether boiler or full, maybe a bit old school but heh ho
 
Basic rule of thumb. If it drops on a tt and there's no smell, with all of the appliances connected, you're OK if it's within limits. Anything else, if it's on an appliance or if you look for the leak by isolating things, no drop allowed.

So I would always do a tt instead of testing at the appliance. Unless the customer wants the leak found or can smell gas.
 
Last edited:
Was this a mini tightness test to check safety controls?

remember a 2mb drop on a tiny section of pipework inside a boiler would not give you a 2mb drop at your meter. Volumes would be a lot different.
 
Last edited:

Official Sponsors of Plumbers Talk

Reply to the thread, titled "maybe a daft question? ..........." which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
nysk2008,
Last reply from
AWheating,
Replies
16
Views
473
Back
Top