Hi, I've went to have a look at a boiler fault several days ago. (FL) flashing.

I understand this to be a flame rectification fault.

I rang Ideal and was told to check the black rectification wire for continuity and got a good reading 1.6 ohms. I removed probe and cleaned. Removed fan and burner, cleaned heat exchanger. Boiler worked fine for a couple of days but now gone to FL again.

Is it time for a new PCB.

Any feedback will be greatly appreciated!
 
For the price of a lead and rec probe, I would change them, if still plays up then PCB.
Explain to customer that your trying to save them money and they won't mind one bit!!!! If lead and probe work, you will be in their good books forever.
 
Yes, to be honest, I was thinking the same thing. Changing the cheaper parts first. I hate the thought of changing PCB to find it's made no difference!!
 
This one has two wires from the black PCB box ..... Black & earth.... Earth going to fan. Black to rectification
 
When I first arrived I removed the bottom plate on the heat exchanger. It was bone dry. Even pulled out an old biro pen which seamed a bit weird
 
  • Like
Reactions: 2 people
I know its a cop out but icos/isars always get the "Better ring ring ideal for a service call" advice. Price of a pcb + labour from us would be more pricey especially with a nice seasoning of doubt.
 
  • Like
Reactions: 1 person
Is it trying to fire or is it coming up at random intervals? I wouldnt go replacing the board just yet they are expensive and chances are it will be something else that you havnt checked yet.

1 Rectification lead can melt and it arcs out to the heat exchanger (this will generally be the cause if it goes to lockout straight away without firing)

2 Check the condense trap for blockages

3 Check the ignition probe as these warp out of shape quite alot this can also cause explosive ignition

4 Actually check the spark (I shut the gas off whip the top off heat ex connect electric to fan and go to fire it up be careful not to get a shock!)

5 If probes look ok check you get power to ignition generator if you do replace that.

6 If you dont get power to ignition generator then start looking at pcb.
 
Hi Millsy, the problem with the boiler is the pump runs, fan runs. You can here it all rev up ignition, fire and then drops off after about 2 seconds.. Had lid off, cleaned rectification probes and spark. Cleaned heat exchanger, checked condense trap. All clear...... Checked harness. 1.6 ohms..
 
Remember not as experienced as you lot so don't shoot me down. Silly question. You are putting the combustion door back on with the four screws before you try to run the boiler aren't you?
 
No, not a silly question but yes, tried with door off and with door on
 
Remember not as experienced as you lot so don't shoot me down. Silly question. You are putting the combustion door back on with the four screws before you try to run the boiler aren't you?
wont make a difference with this heap,Merv,worth checking the det probe lead to pcb routing they can chaff on the combustion box entry point and also get trapped on the drop down pcb retaining bracket if the pcb,s been changed before(highly likely it has)
 
Hi Millsy, the problem with the boiler is the pump runs, fan runs. You can here it all rev up ignition, fire and then drops off after about 2 seconds.. Had lid off, cleaned rectification probes and spark. Cleaned heat exchanger, checked condense trap. All clear...... Checked harness. 1.6 ohms..

If it is actually firing up then I would be looking rectification probe or probably what I should of put as no 1 gas inlet pressure.
 