Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Install the app
How to install the app on iOS

Follow along with the video below to see how to install our site as a web app on your home screen.

Note: This feature may not be available in some browsers.

finchy01

Plumbers Arms member
Plumber
Gas Engineer
Sep 13, 2009
192
24
18
Farnham. Surrey
Member Type
Heating Engineer (Has GSR)
Here's one. If I service a domestic boiler in a pub. As long as gas pipe is 35mm or under etc how is this classed domestic or commercial? I only have domestic ticket so obviously wanted to check.
 
Boilers? What's the combined output and is there a sub meter?

Unless the kitchen has its own supply?
 
If the boilers on a leg with its own aecv. And that leg is within your tickets your good to go.
 
If the boilers on a leg with its own aecv. And that leg is within your tickets your good to go.

If it's off a commercial installation you would still need the commercial ticket. Unless it's off a sub meter with a domestic sized installation off that

We don't even know if this is or isn't one though yet.
 
Last edited:
If the boilers on a leg with its own aecv. And that leg is within your tickets your good to go.

If it's off a commercial installation you would still need the commercial ticket. Unless it's off a sub meter with a domestic sized installation off that

We don't even know if this is or isn't one though yet.
 
Last edited:
I looked into this. Nope. It the leg with its own aecv has suitable test points and that leg falls within 1b then you can. Absolutely 100%
 
  • Like
Reactions: 1 person
If the pub is covered by 1B then he should be fine anyway.

I was of the impression that he was uncertain of the size of the installation.

If it's a pub it is unlikely that it will be a large installation but it depends how big a pub and what is installed.

The AECV point you make phil, would not be correct in all cases. It only counts with 21Mb OP at primary meter outlet and installations under the 0.035 vol. So it isn't a general rule
 
The AECV point you make phil, would not be correct in all cases. It only counts with 21Mb OP at primary meter outlet and installations under the 0.035 vol. So it isn't a general rule

Yes, he stated a domestic boiler and i was talking in reference terms to that as its always gonna be that OP unless LPG for a dommy boiler
 
  • Like
Reactions: 1 person