Went to service a boiler today.
First tests I do is tightness/letby and then working pressure at meter and inlet on gas valve.
I was getting 10mbar at the meter working pressure. They only have the boiler, no other appliances in gas.
Boiler is a Worcester Greenstar 40CDi conventional.

Called transco as could have been a dodgy regulator. Or undersized pipework but I wanted to rule out the regulator first as standing pressure was only 21mb.

They attended when I wasn't there and changed the regulator but said nothing was wrong with the old. But they tested the meter/pressure when the boiler was in 'condensing mode' - you know when you restart the CDi's and it does the minimum rate thing for about 20 mins.

So he got a normal reading, as did I on minimum rate. But as soon as it got to max rate went straight to 9.5mb at the meter.

Turns out the run needs upping from 22 to 28 - apparently a guy did a new run which is about 9 meters with let's say 8 elbows in 22 and said everything was fine. They'd also left a 4m run of pipework completely unsupported practically hanging in mid air.

Question: do national grid have to know about boilers? Surely they'd know the boiler was in min rate mode and should have waited for max rate to kick in? Or do they rest the regulator differently?

Have turned off the boiler. Owner is gutted as they've just paid £30k having the kitchen tiled in cement tiles which is over the new gas run. Oops!
 
If your getting 9.5mb at the meter, not the boiler. There is a problem with the main supply.
 
No as all he was doing was purging the gas through while he was there anything from the meter not there problem

That's why if they find leaks on existing Pipework gets capped and cus gets a sheet saying you need s gas engy as you have a leak

but you need a min of at least 18 at the meter
 
Last edited:
No as all he was doing was purging the gas through while he was there anything from the meter not there problem

That's why if they find leaks on existing Pipework gets capped and cus gets a sheet saying you need s gas engy as you have a leak

but you need a min of at least 18 at the meter

Ahh ok..

Question:

How is it possible to be getting 10mb at meter working pressure, 8mb at inlet on gas valve working pressure but correct heat input and gas rate readings????
 
Yes mate.
If it's been fine until recently. It could be a faulty governor, or a problem with the main. Is there any gas work ( new main etc) being done locally?

No gas work being done. And transco put a new regulator on today. Boiler hasn't been checked in 2 years so not sure.
 
Ahh ok..

Question:

How is it possible to be getting 10mb at meter working pressure, 8mb at inlet on gas valve working pressure but correct heat input and gas rate readings????

I would say reg faulty as can't handle the demand but Pipework loss looks right just working pressure down

If meter working pressure below 18 grids problem

Get them out with you there
 
Last edited:
I would say reg faulty as can't handle the demand but Pipework loss looks right just working pressure down

If meter working pressure below 18 grids problem

Get them out with you there

Could undersized pipework cause a low working pressure at meter?
 
But they put a new one on today and I rechecked it, same thing

Didn't check on full load

And are you sure they changed the reg ?? Also could be some dirt has gotten into there line and blocked the new reg again

It's down to them so get them to sort it best for you to be there if pos, do your max while he's there
 
Didn't check on full load

And are you sure they changed the reg ?? Also could be some dirt has gotten into there line and blocked the new reg again

It's down to them so get them to sort it best for you to be there if pos, do your max while he's there

On way back now
 
Didn't check on full load

And are you sure they changed the reg ?? Also could be some dirt has gotten into there line and blocked the new reg again

It's down to them so get them to sort it best for you to be there if pos, do your max while he's there

Def somethings wrong. 25.5mb standing
12mb working on max rate at meter
 
Ahh ok..

Question:

How is it possible to be getting 10mb at meter working pressure, 8mb at inlet on gas valve working pressure but correct heat input and gas rate readings????

Because it forced combustion (fan driven). I wouldn't be too hasty with the loss across installation as 2mb from meter to gas valve test point is permitted (potential 1.5mb loss from appliance iso to gasvalve if I'm not mistaken). Almost certainly undersized service pipework probably been inserted with serviflex, they use 16mm most of the time and it's way too small. When you next bump into a NG engineer ask for an ecv test point. It allows you to take a working pressure before the regulator and proves beyond doubt what the issue is. Last time I spoke with the grid they said as far as they go is turning a tap on or turning on a room stat if not a combi, they dont put appliances in forced max rate. Hope this helps.
 