Sounds about right including gas valve test point press drop but even if pipework was undersized you should still get a working pressure at the meter within spec regardless Jay.10mbar meter
8 mbar boiler
so not a million miles out
Sounds about right including gas valve test point press drop but even if pipework was undersized you should still get a working pressure at the meter within spec regardless Jay.
How are you measuring pressure - digital or manometer. Water guage or single sided. If single sided you have got right fluid in. I know you had an issue the other week with a vaillant.
Undersized internal pipework was NCS providing safe working of all appliances can be achieved. Now is just a recommendation. And how can you test the internal pipework with an AR meter installation? Tell them you've done your calcs and the internal run is satisfactory. At the end of the day the customer is paying for a service they are not providing them with ie 6m3 at 21 +/- 2.
I use a regin premiere gauge with the regin fluid. I double checked my gauge on my meter at home and it's working fine.
Thing is, at gas college, teacher said if all appliances are on and pipework is undersized the working pressure can drop below the nominal. Is this not true then?
Your problem is either a blockage in main or undersized main.
The Nat Grid would have turned that off if they had seen it so low and investigated it.
They won't go around messing with appliances to set them on full rate. If you have an issue like that, you'd be best to arrange to meet on site and you ensure that you set the appliances running on high rate.
The internal pipe work is nothing to do with it by the sounds of it.
The only way that internals could effect the service is if you're pulling too much gas through it for it's size.
There is one stupid exception. Im sure youve heard the "peak time" caveat.
Otherwise if overall demand is upto 6m3 on a typical domestic meter then it should pretty much be in the ballpark at the meter.
Yeh there is no definition of a peak time - thats whats stupid about it.
Not sure try bes
give me tonight have a mate who works for national grid, will see what he says
Did you manage to speak to your mate Shaun?
He also said the boiler could be pulling too much gas through the pipework.
yes he said its strange and not uncommon for that excuse
So call them back out? Either way I have to upgrade the pipework so may just wait until that part is done then they have no excuse
problem is that wont fix it, best have a word with your cus as there paying your bill
from the meter how much exposed pipework can you get at?
About 4m in the basement from meter then disappears under flooring
up that first as the rest aprox 6 m with 2-4 elbows should be fine
I just did the same calculation and thought the same!! Hopefully they'll not be more elbows than that - cheers Shaun