Thanks Ric - much appreciated!Sounds like Marty basically knows his stuff. I'm not expecting an explosion.
So I'm basically asking can I connect the flow pipe (bottom pipe with drain cock) to the one above (return) using elbow fittings and auto bypass?
TRVs on rads can shut down so that's why you need a bypass on all-TRV systems. If the boiler has its own bypass then that external bypass is confusing me. I'm wondering if it has a valid technical raison d'etre, or if it was installed in a misguided attempt to ?
Any chance of a pic of the boiler ?
Thanks mate. I'm not at home but I can confirm that the boiler is a Valliant Ecotec 28 combi boiler. Do you you need a photo of the pipe work underneath or something?
Thanks again
Ok guys. So if you were me would you be installing a auto bypass valve on the system even though there is an internal one? I'm not sure whether or not the isolater valve was there before the combi boiler was installed back in 2015.