Hi,

I have an older style open vented heating system with a Glow worm 50/60 RF flued fan boiler. I have a hot water tank on the first floor and two header tanks in the loft, one large for the hot water and a smaller one for the heating.
Last week I removed a radiator from the landing and capped off the pipes under the floor. Since doing this when the boiler switches off there is a loud bang and the whole heating system shakes. I thought it was an air lock but I have bled the system and all radiators are warm. It only does it when it's on heating, not when on hot water. Another point, when the boiler switches off water runs into the header tank for about 3 seconds.p from the expansion pipe.
I've even tried connecting the pipes I cut off together just in case I had messed up the flow and return but it's still the same. All radiators have trv's apart from a heated towel rail in the bathroom and large radiator in the hall which is by the thermostat.

Anybody have an ideas what it might be. I have also flushed the system and it is clean. It's worked fine for years until I removed the radiator.

Many thanks.

Paul.
 
Do you have an automatic bypass on the system. You may need it if the radiator you removed acted as manual bypass.
 
It sounds like a spring return motorised valve slamming shut.
Vee may well be right with the bypass but you need to identify the cause first.
If you have a motorised valve, check it when you turn the heating off to see if it’s that, which is making the bang.

If not let us know and we’ll think of something else
 
It may not have one. I was going off the description you gave. Difficult on a forum.
Normally, airing cupboard or near Boiler !

If it hasn’t got one, maybe an auto bypass is the answer.

Any chance of photos of Boiler and airing cupboard ?
 
It sounds like a spring return motorised valve slamming shut.
Vee may well be right with the bypass but you need to identify the cause first.
If you have a motorised valve, check it when you turn the heating off to see if it’s that, which is making the bang.

If not let us know and we’ll think of something else

It has two motorised valves. I can hear the motors opening and closing when both the heating and hot water are in use. The bang is really hard to identify, it seems to be coming from around the pump but difficult to say for sure. Is the hot water being pushed up into the header tank part of the same problem.

When I removed the radiator I capped the ends and have also tried connecting them together similar to how the radiator would function but no joy.

Thanks for your advice.

Paul.
 
It has two motorised valves. I can hear the motors opening and closing when both the heating and hot water are in use. The bang is really hard to identify, it seems to be coming from around the pump but difficult to say for sure. Is the hot water being pushed up into the header tank part of the same problem.

When I removed the radiator I capped the ends and have also tried connecting them together similar to how the radiator would function but no joy.

Thanks for your advice.

Paul.
It has two motorised valves. I can hear the motors opening and closing when both the heating and hot water are in use. The bang is really hard to identify, it seems to be coming from around the pump but difficult to say for sure. Is the hot water being pushed up into the header tank part of the same problem.

When I removed the radiator I capped the ends and have also tried connecting them together similar to how the radiator would function but no joy.

Thanks for your advice.

Paul.

Honeywell ( silver box top ).?
 
IMG_3155.JPG


The boiler is in the garage 15 meters from the airing cupboard. Since this problem the bleed valve no longer works and is full of water. If you undo the screw water overflows from the nipple.

Cheers.


It may not have one. I was going off the description you gave. Difficult on a forum.
Normally, airing cupboard or near Boiler !

If it hasn’t got one, maybe an auto bypass is the answer.

Any chance of photos of Boiler and airing cupboard ?
 
Yes it needs a bypass.
If you try holding the valve open whils someone turns heating off you’ll see if it stops the bang
 
IMG_3156.JPG
View attachment 31460

The boiler is in the garage 15 meters from the airing cupboard. Since this problem the bleed valve no longer works and is full of water. If you undo the screw water overflows from the nipple.

Cheers.
The
Yes it needs a bypass.
If you try holding the valve open whils someone turns heating off you’ll see if it stops the bang

How would you do that, I'm not sure. Presume you would take the cover off but then what?
Many thanks.
 
Opposite side to the label on the zone valve is a little lever. When your heating is on there should be no resistance on the lever and it should move left and right freely. Heating off and you should feel tension on the lever and when you move it is should move back to close position on a spring action. Switch your heating off and hold the lever open. If there's no bang once the pump has shut off then you def need a auto bypass. There is also a little nib on the valve where you can hook the lever onto so it won't return to close, if you are doing this alone.
 
Opposite side to the label on the zone valve is a little lever. When your heating is on there should be no resistance on the lever and it should move left and right freely. Heating off and you should feel tension on the lever and when you move it is should move back to close position on a spring action. Switch your heating off and hold the lever open. If there's no bang once the pump has shut off then you def need a auto bypass. There is also a little nib on the valve where you can hook the lever onto so it won't return to close, if you are doing this alone.

I'll try it in the morning and be in touch then (kids asleep). Thanks for your help and advice, much appreciated. Regards. Paul.
 
When the heating is on, there shoul be no tension as the valve is open. If it is calling for heat that is.
i.e. programmer on, room stat up above room temp.

Maybe you meant that ?

If it still bangs with the valve left open, it needs looking at, I can’t guess without witnessing it.

I don’t think it’s an air lock but that is my opinion.
 
When the heating is on, there shoul be no tension as the valve is open. If it is calling for heat that is.
i.e. programmer on, room stat up above room temp.

Maybe you meant that ?

If it still bangs with the valve left open, it needs looking at, I can’t guess without witnessing it.

I don’t think it’s an air lock but that is my opinion.

Sorry was checking the wrong one. You are right, no resistance when on. I held it open, turned off and no bang. Can still hear water going into header tank? Does this mean the valve is faulty.

Cheers
 
Sorry was checking the wrong one. You are right, no resistance when on. I held it open, turned off and no bang. Can still hear water going into header tank? Does this mean the valve is faulty.

Cheers


It can be a faulty valve yes but in your case I would suspect that the lack of a system bypass is causing the valve to slam shut as the pressure increases on closing. (valve damage may have occurred as a result of not having a bypass).

My advice:-
Install a system bypass (22mm Auto) and see if it stops the bang. If not replace the valve. You need the bypass anyway.
 
Agree with the above but as your draining down I would replace the valves at the same time, if you can afford the slightly extra cost
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Heating Bangs when switching off." which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread starter

Joined
Location
Kidderminster
Member Type
DIY or Homeowner

Thread Information

Title
Heating Bangs when switching off.
Prefix
N/A
Forum
UK Plumbers Forums
Start date
Last reply date
Replies
78

Thread Tags

Tags Tags
heating

Thread statistics

Created
Paul Cooksn,
Last reply from
Paul Cooksn,
Replies
78
Views
26,791

Weekly or Monthly Email Digest

Back
Top