My Logic Combi 30 Boiler was working fine. Whilst servicing it, the hot water stopped firing up although the heating still works. . Engineer said these cheap boilers often do this when turned off and back on again and now it needs a flow something. Is this correct please? He also had a leak...
Hi lads any of use ever come as an L3 on a logic? Nothing at all in the book about it just all pointed towards board when I was there, swapped it inc code plug, swapped thermistor whilst I was there and all that's done is I can now run just hot water for about 15 mins ... before it was heating...
morning
as told by my local ideal rep if the boiler has a serial number earlier that AFQ meaning it was manufactured on June 2019 or before you will be unable to use/bind the new Halo combi stat
Gas engineer here. Been to an ideal logic combo 24, (the older model with brass manifolds either side) customer complained about temperamental hot water. Did the usual checks solid red light on hall sensor diverter head ok diaphragm springs back return thermistor above pump ok thought it must be...
IDEAL LOGIC COMBI 30, hot water not very hot, water flow fine. Would I be right in that the diverter valve cartridge needs replacing. Any other suggestions
Hi, my Mum's Ideal Logic combi keeps cycling when the temp reaches 50 degrees despite the CH control set to max. The manual says the flow temperature should reach 80 when set to max but I can actually hold the CH feed pipe with my hand and it never gets hot enough to cause me to let go before...
Hello
I'm struggling to understand this code as I cant find it in the User Manual. The display has an SE code with a spanner in the top left corner. I am not able to change the water (40 degrees)or central heating temperature (30 degrees). Does anybody know what this could be?
Thanks
Hi,
I need to replace a bath tap but the taps don't have any shut-off valves, I can do the cold water but not certain how to do the hot.
My boiler is a logic combi 30 pressurised system, how do I stop the water from flowing while I replace and will I need to fill the system again.
Thanks
Hello
I have a Ideal Logic Plus Combi which is approx 2 1/2 years old.
I am waiting for the Gas Engineer to come out but in the meantime would like to have some idea what might be up with my boiler.
There are a 2 main issues and i don't know if they are related.
Firstly the hot water only gets...
Hi, we have an ideal Logic combi 30 and have an issue with the system loosing pressure. We have had an engineer look at the system twice without being able to find a fault.
I isolated the boiler last week to determine it was the boiler and not the rest of the system.
When the system was warm...
Hi all,
Boiler has been losing pressure for overnight for a couple of days. Was at a loss, but have just found this on the pipe loop outside of the house in line with where the boiler is sited. What is its purpose?
Second pic is where I presume the pipe comes from. It connects to the very Last...
Hello all.
I had the annual service for my Logic Combi 30 boiler back in November and all was seemingly fine. However since the colder weather has really begun within the past few weeks we have had the heating on more and at a higher temperature (22.5, up to 24 degrees on occasions). As the...
Hi all
First timer here - after reading a lot of the advice present I thought it would make sense to get stuck in and throw something into the ring.
I am a Landlord and Agent operating new build properties in the Nottinghamshire areas, and have what seems to be an ongoing problem with one...
Ideal logic combi
Anybody had issues with the bottom of heat exchanger blocking - first thought was air/ gas ratio ,but found when removing condensate trap completely including rubber connection elbow noise on initial fire up stopped ,as boiler was getting air it needed, flushed with boiling...
A routine vist to service this boiler a first time for me, turned into a bit of a nightmare as you can see below a small hole had appeared in the plastic flue part that takes the condense away made a right old mess in there i did a temporary repair job and serviced a full safety check it all...
This boiler was flooded through the condense drain which was connected to a gutter downpipe that was blocked at the end. The people came home to a flooded kitchen. Water came back up the condense tru the trap up the heat exchanger and out tru the fan and gas valve connection imside the casing...
A mate tells me he cured a heat engine leak on this boiler (confirmed by boiler isolation & dripping condensate drain) by adding K-Seal car type sealant, and It's still ok after 5 years. Has anyone else had success curing these leaks with sealant additives?
Ideal Combi bolier. When I repressurise the system to 1bar it almost immediately dumps the water out the condensate pipe before even switching in on at mains. HELP!