Sorry I posted this in the wrong thread.Plumber had gone for a 24kw now as that’s the same as the old one.
What was it at the meter with the boiler running flat out?CH guy was here today fitting the hob. I said the boiler was niggling me and asked him to show me.
He stuck his manometer on the boiler and showed me it reading 23mbar with the boiler apparently running "flat out".
It was at the boiler.
The trouble is, I know enough to feel uncomfortable about this, but not enough to argue with the CH guy, who clearly thinks I'm being completely ridiculous and there's absolutely no question in his mind that it's perfectly fine.
Is 23mbar at the boiler normal? I thought it was 21mbar typically.
I'm simply going off the tables that say the length plus bends etc of the 15mm tube can't carry enough gas for the boiler's max demand.
Typical U6 Meter on low pressure domestic service would be expected to be 21 mbar outlet working +/- 2 mbar.
They can be different, this is what is typical/expected.
You would expect (by design) a drop of 1 mbar meter to appliance working. This too can be different dependent on a number of factors but still be deemed acceptable. You'll have to trust me on that. Not got time to go through the technicalities.
You obviously have concerns. In my opinion you need a second opinion or to make it official, you would need to contact Gas Safe. If they do come to inspect the work, they will want the installer on site during the visit so you might want to discuss this with him and explain why you are considering it. Just to give him chance to go through it with you in enough detail to put your mind at ease.