I have NuHeat UFH system, and this has no Thermostatic Blending valve on the heating circuit. (Heat Master II cylinder has pick up coil)
Nu-Heat System installed -

This means I can't run store above 60C due to risk of overheating UFH pipes.
I want to add a Thermostatic Mixing valve so have bought a 28mm UFH Thermostatic Valve.
I have a question as to location ...
Temperature is limited by the thermostat on the Thermal Store to 60C
Water is pumped on Return circuit from distribution manifolds for the UFH
To aid in boiler efficiency and solving some other issues, I intend to add a 28mm Thermostatic Mixing valve .... The first picture represents position a 'as is'

My preferred option is OPTION 1
Easiest as pump and pressure relief etc. need not be moved

Or alternate is Option 2
This pumps out the mixed water from the valve .. so change the pump onto flow not return.
A lot more work to achieve.

Welcome thoughts from those that know ... or in fact does it make any difference.
Nu-Heat System installed -

This means I can't run store above 60C due to risk of overheating UFH pipes.
I want to add a Thermostatic Mixing valve so have bought a 28mm UFH Thermostatic Valve.
I have a question as to location ...
Temperature is limited by the thermostat on the Thermal Store to 60C
Water is pumped on Return circuit from distribution manifolds for the UFH
To aid in boiler efficiency and solving some other issues, I intend to add a 28mm Thermostatic Mixing valve .... The first picture represents position a 'as is'

My preferred option is OPTION 1
Easiest as pump and pressure relief etc. need not be moved

Or alternate is Option 2
This pumps out the mixed water from the valve .. so change the pump onto flow not return.
A lot more work to achieve.

Welcome thoughts from those that know ... or in fact does it make any difference.