I have a problem with air being sucked into my CH system creating airlocks in the radiators. The water is flowing back into the FE tank via the cold feed pipe. I can feel warm water coming through the feed pipe back into the tank as the tank water level slowly get higher. I can hear the overflow gurgling in the FE tank.

The system is 20 years old but the Worcester Bosch boiler is only 9 years old. All has worked perfectly well. I did have the classic blockage where the cold feed meets the hot return but the clogged pipes have been cut out and replaced.

I have fitted a new pump and it is set to the lowest speed. All of the radiators have been bled many times and balanced.

So the heating is working fine except that I have this problem of the air displacing the water back to the FE tank. The water it getting back into the tank a quite a rate - I would say about 2 litres per hour. This means that the rads need to be bled constantly.

Any ideas? Could it be an problem with the boiler itself?
 
At 6l/m the old UPS 15/50 had around a 3m head and the UPS 15/60 around 3.6m head.

The very old Selectric UPS 15/50 and Super-Selectric 15/60 has 7 and 9 foot head, at 6l/min respectively, so a little less. (I say 'has' in the present tense because I know at least one that is still running.)

All the above are on speed 1.

I suppose it would be useful to plot a little chart showing various types of pump curve all on the same axes, so comparisons could be made.

Why am I still up?
 

Attachments

  • Informative
Reactions: John.g
At 6l/m the old UPS 15/50 had around a 3m head and the UPS 15/60 around 3.6m head.

The very old Selectric UPS 15/50 and Super-Selectric 15/60 has 7 and 9 foot head, at 6l/min respectively, so a little less. (I say 'has' in the present tense because I know at least one that is still running.)

All the above are on speed 1.

I suppose it would be useful to plot a little chart showing various types of pump curve all on the same axes, so comparisons could be made.

Why am I still up?

Will put together one (chart) later today, I will include my own old Salmson NYL 33 which I installed in Sept 2000 set to speed 2 and was still running perfectly and quietly when I replaced it last November with a Wilo Yonos Pico 1-6 last November.
 
  • Like
Reactions: Ric2013
A bit off thread but I love this forum! It's so good to see people discussing issues using reasoned and evidenced facts supported by experience rather then slagging each other off.
 
  • Agree
Reactions: Pickwickpick
A bit off thread but I love this forum! It's so good to see people discussing issues using reasoned and evidenced facts supported by experience rather then slagging each other off.
That's because I'm a left-leaning liberal **** as they say on Youtube when I'm trying to make a reasoned point.
 
  • Like
Reactions: Pickwickpick
Will put together one (chart) later today, I will include my own old Salmson NYL 33 which I installed in Sept 2000 set to speed 2 and was still running perfectly and quietly when I replaced it last November with a Wilo Yonos Pico 1-6 last November.

Here it is, I wouldn't care to be running a few of these on even fixed speed 1, especially the UPS 3 .
 

Attachments

Doesn't work on Libreoffice. Thanks though.

Here's a snapshot of it & also a Zipped word copy.

upload_2019-1-21_18-18-33.png
 

Attachments

I take it that's the old UPS and not the very old one, but it looks wrong. The UPS 15-50 starts at a 0 flow at 3.5m exactly, so how are you getting 3.76? Have you yet another IOM, as that differs from my data?
 
I take it that's the old UPS and not the very old one, but it looks wrong. The UPS 15-50 starts at a 0 flow at 3.5m exactly, so how are you getting 3.76? Have you yet another IOM, as that differs from my data?
You posted
I take it that's the old UPS and not the very old one, but it looks wrong. The UPS 15-50 starts at a 0 flow at 3.5m exactly, so how are you getting 3.76? Have you yet another IOM, as that differs from my data?

I got it from one of your files above... "Selectric UPS Old Style" page 1 shows speed 1 curve starting at 3.75/3.76M ?.
 
Last edited:
At 6l/m the old UPS 15/50 had around a 3m head and the UPS 15/60 around 3.6m head.

The very old Selectric UPS 15/50 and Super-Selectric 15/60 has 7 and 9 foot head, at 6l/min respectively, so a little less. (I say 'has' in the present tense because I know at least one that is still running.)

All the above are on speed 1.

I suppose it would be useful to plot a little chart showing various types of pump curve all on the same axes, so comparisons could be made.

Why am I still up?

Can you post any links (charts etc) to a UPS 25-50 Selectric, power outputs 40W, 65W & 95W. (installed in a new build house in 2005/2006), still running.
Thanks.
 
You posted


I got it from one of your files above... "Selectric UPS Old Style" page 1 shows speed 1 curve starting at 3.75/3.76M ?.
Can you look at the chart on my file again and tell me what you see? I make it between 3.5 and 3.6 and would like to know if this is human or electronic error.
This is how it appears on my screen:
system1.jpg
 
Can you look at the chart on my file again and tell me what you see? I make it between 3.5 and 3.6 and would like to know if this is human or electronic error.
This is how it appears on my screen:View attachment 36507

(Internet down for past few hours so couldn't relpy)

A bit confused as to why you ask human /electronic error as this I presume is a grundfos data sheet that you posted?, I just copied the data from it into my own spreadsheet, if you can post the proper chart I can incorporate that data in the spreadsheet and re post.
 
It's okay John. I'm not very good at reading data from a screen for some reason and I was reading the digits 3.5 against the 3.75 line.

So ignore my comments above.

No problem, if you do come across any info on that 25-50 selectric with those power settings I would appreciate it. (#70)
 
Can you post any links (charts etc) to a UPS 25-50 Selectric, power outputs 40W, 65W & 95W. (installed in a new build house in 2005/2006), still running.
Thanks.
The curves are exactly the same as for the UPS 15-50 Selectric of the same vintage. The innards are the same, it's just the connections which are different.
 
The curves are exactly the same as for the UPS 15-50 Selectric of the same vintage. The innards are the same, it's just the connections which are different.

ref post#61
File "selectric UPS pumps old" shows the UPS 15-50 with power inputs of 35/45/50 watts. In "selectric very old" it shows the UPS 15-50 with power inputs of 40/65/100 watts with different speeds/curves, my query pump, a UPS 25-50 has power inputs of 40/65/95 so I will assume that the pump curves are similar to the latter one, above, its a 2005/2006 install. I wonder what was the time span period for the UPS 15-50 35/45/50 watts.
 