Any reason 1/2" Portsmouth (Part 1 ballcocks or FOV) are still sold at all?

View the thread, titled "Any reason 1/2" Portsmouth (Part 1 ballcocks or FOV) are still sold at all?" which is posted in UK Plumbers Forums on UK Plumbers Forums.

Ric2013

Plumbers Arms member
Plumber
To cut a long story short, I started reading the the WRAS Water Regs book again:

G16.1 d states that a G1/2 size valve (do they mean a 1/2" valve as opposed to, say, a 3/4" valve?) must be 'constructed so that the water shut-off level may be altered [...] without bending the float lever.' So why bother making Part 1 valves of that size at all?

I suppose you could argue that replacing a valve does not constitute installing one so you can fit a non-compliant valve as a replacement? Is that why these are still sold?

Just wondering as usual 🙂

Thanks,

Ric
 
Last edited:
Part 2's are only made in G1/2 & 3/4 sizes so if you want anything bigger it is still the Part 1.

Also Part 2 is limited to the orifice size that can be fitted I seem to remember.
 
Many existing WC cisterns still in use have a Portsmouth float operated valve (part1), when the valve is in need of replacement the use of a part2 will not fit due to its air gap back flow protection of the water outlet at the top by means of the bent plastic water delivery spout sticks up too high for the cistern lid. The part 1 can be installed providing back flow protection is installed in the supply pipe in line with The Water Supply (Water Fittings) Regulations 1999.
 
Many existing WC cisterns still in use have a Portsmouth float operated valve (part1), when the valve is in need of replacement the use of a part2 will not fit due to its air gap back flow protection of the water outlet at the top by means of the bent plastic water delivery spout sticks up too high for the cistern lid. The part 1 can be installed providing back flow protection is installed in the supply pipe in line with The Water Supply (Water Fittings) Regulations 1999.

Where I've seen this though I just replace them with a side entry adjustable arm float valve tbh.
 
Again if there is space, I would update to part 2 unfortunately at times someone has cut the hole in the F & E to near the top.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Any reason 1/2" Portsmouth (Part 1 ballcocks or FOV) are still sold at all?" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
Ric2013,
Last reply from
moonlight,
Replies
10
Views
4,074
Back
Top