Evening guys,

I have a customer with an Ariston Genus HE24 with a fault code E34 which says that the air pressure switch isnt shutting off. Also the water temp only goes up to 52 degrees then shuts off instead of staying constant. I have changed the APS and the HW sensor to rule them out as they are relativly cheap.

There is obviously an air flow problem either with the flue (which runs away from the boiler down hill) or the fan. Although the fan seem to be fine.

Ill get to the bottom of it tomorrow but thought I would ask if anyone has had a similar / same problem.

The boiler is only 4 years old and a shocking installation which I can guarantee hasnt been flushed!!!

Any info would be great. Cheers!
 
remove the restrictor ring within the recuperater(secondary exchanger bolted to fan) if its not in there it will be in the flue bend i take it you have checked the venturies?
 
Im going along tomorrow so thought I would ask. Recuperater? venturies? jesus.....new boiler! lol

I also forgot to say that when I put the casing on the boiler extinguishes but when I remove it it lights!
 
its easy to get the fan out to get to the recuperator(one screw and pressure tubes off +wires) ,if there's a ring inside it remove and discard while the fans out check the venturie should take around 20 mins recuperators the big silver and black lump bolted to the fan,venturies the jet the aps positive tubes connected to

and working ok with the combustion door off are classic symptoms of the above restrictor ring at fault
 
Last edited by a moderator:
no probs come back and tell us if it fixes the microgenus it will help other engineers
 
is it a genus or a microgenus, they are 2 totally different boilers. i think u have 2 seperate faults. the e34 that happens with the case on but not the case off is probably to do with air flow. the flue might be blocked or the inner flue might be broken along its length. (this can be checked using a flue gas analyser in the air inlet, u should get no co2 readings coz it should be clean air, if you get a co2 reading then it's dissconnected somewhere along it's length and the fumes are mixing with clean air). The hot water only getting to 52 degrees could be the secondary heat exchanger blocked. you can find this out by checking the primary temperatures. if the primarys are getting up to 80 degrees and the hot water is only getting to 52 then it's not transfering it's heat and it's probably blocked and cutting out on overheat. the primary temperatures for the genus can be checked in the parameters around the 800's. look in the manufacturers instructions at the back. you have to type in 234 first then the parameter you want.
 