right ok...just looked at pic again,ksareen. You are right in saying that the 15mm pipe on the right is a cold feed...but this is the cold feed to the feed and expansion tank.
The cold feed i am referring to is the cold feed to the heating system which is shown on your pic 1, the one with the gate valve on coming from the bottom of the f & e tank.
This 15mm pipe tees into the 22mm pipe which is acting as the cold feed and expansion pipe for the central heating system. The blockage could well be in or around that tee....first place i'd try the magnet test on, i would then trace the 22mm pipe downwards with the magnet to see what you can find.
The gate valve in your lastest pic is the bypass for the central heating system,another place where i have found blockages in the past.
i hope this helps.