Insulation tests do not tell you how good the earth is just that one wire is insulted from the other and how good that insulation is. An Earth loop test tells you how much current your earth path will take. It would be point less earthing with fine wire it would burn out if you got a 230 volt 13 amp fault discharging to earth and leave your pipework still live and able to deliver a big shock for anybody touching it.
The RCD is intended to sense the current is the same voltage in both the Neutral and Positive wire in the cable. If its equal it stays open, if its more in one wire than it is in the other it shuts down because in an AC system it means the current is running to earth somewhere. But its relying on a mechanical RCD to always be working and not seized up over many years. That is why they have test buttons on them that should be tested every month or so. But who does?
It is right though, you do not have to supplementary bond providing the pipework is connected somewhere along its length to the main Earthing point and protected by an RCD. But how would you know it was connected without testing the earth and how good was the connection?
Anyway as Tamz says its not our job, but its interesting.
I am sorry you seem to be having trouble understanding me scoobydoo in my explanation of electricity and how it and earth bonding is supposed to work. I am not saying I am right and sambotc is wrong, we are talking about two different tests.
Please go careful scoobydoo and look up Earth loop testing as well as electrical safety testing and why they are done for both your own safety and your customers.
Don't get me wrong I am not advocating plumbers conduct these tests except the basic boiler safety electrical test which they are advised to do after a boiler repair and for which an insulation tester may be very handy. The question was about earth bonding not insulation testing.
I was alluding to the quality of earth and the amount of earth fault charge it can take. Sambotc was referring to the quality of the insulation isolating the wires from each other. They are two different things.
Most MI's will tell you a basic electrical safety test is required on a boiler after any electrical repairs. 🙂 🙂
Can't argue with that, glad to hear that I have the right end of the stick as it is often discussed in much detail in electrical forums by qualified electricians with some confusion.
Can you confirm whether or not there are any regulations regarding bridging plastic fittings within BS7671 as I can't find it! Surely it depends what the fitting is on and whether or not it forms part of the main equipotential bonding or supplementary bonding? If the later then I would imagine a plastic fitting would actually help as it will increase resistance and lower the potential?
I was tying to inform the original writer not cause a problem. I am not getting confused at all. Ask yourself what purpose supplementary bonding serves if it is not connected to a low resistance earth path? The 17th edition requires main equipotential bonding to be in place as well as RCD's, if it is not, you may have to bond as per the 16th.
To me it sounds silly not to check the quality of earth as well as its continuity. An earth loop test does both.
You may for instance find yourself in a house with the bonding done in the bathroom so you figure its okay. However the pipework may not have a path to the main house earthing terminal. So a fault current cannot freely flow to earth and cause the disconnect. Until that is you get hold of the pipe yourself and I have been in that situation. The electricity finds it easier to go through you than down the metal pipework.
However as a plumber, you are not usually required to do anything about it, just be aware of the problems. A simple Neutral to Earth and Phase to Earth test using a voltage test lamp should show up any problems. But go careful doing the test for as an earth Loop test it may make anything connected to the earth system live. Phase to Earth should light the test lamp, Neutral to Earth should not.