I may have been looking at the CDI classic which says...Gas Flow rate- max 10 minutes after lighting.

It says the same for the CDI 35 model 47 311 94 & the CDI 40 model 47 311 95
That's not saying that the boiler needs 10 minutes to reach max output. It's just telling the engineer to wait 10 minutes before carrying out a gas flow rate test. It's similar, but not exactly comparable, to letting a car warm up before doing an emissions test.
 
  • Like
Reactions: John.g
That's not saying that the boiler needs 10 minutes to reach max output. It's just telling the engineer to wait 10 minutes before carrying out a gas flow rate test. It's similar, but not exactly comparable, to letting a car warm up before doing an emissions test.
You have quite a good understanding of your boiler sir , but its far to big for the 9kw of radiators connected to it , any good GSI should be able to down rate that boiler this will not affect the hotwater . Kop
 

Attachments

  • Screenshot_20191212-071841_Drive.jpg
    Screenshot_20191212-071841_Drive.jpg
    98.4 KB · Views: 44
You have quite a good understanding of your boiler sir , but its far to big for the 9kw of radiators connected to it , any good GSI should be able to down rate that boiler this will not affect the hotwater . Kop
I have read that in the installation manual, but the Greenstar CDi Service booklet says this:

37cdi range rating.png


I have taken that to mean that the 37 and 42 versions are not adjustable; but now I'm not so sure. The current value is 82% and it doesn't change to 100% if I reset the boiler using function 8E. (I made a note of all parameters before resetting, in case any had been changed by the installer. They hadn't.)

So does the "not on 37 and 42 combis" just mean that they are not adjustable above the default setting? Looking at the data tables for the CDi range, I'm beginning to think it does. Very confusing. There's only one way to find out ...
[automerge]1576250104[/automerge]
The current value is 82%
That was quoting from memory; it's actually 84%.

Using heat input figures (output isn't suitable as it varies with condensing), the maximum input is 37 kW for HW and 30.9 kW for CH. So the CH output is 83.5% of the boiler's max output, which is near enough to 84% when the display only shows two digits.

I have down-rated the CH to 35%, which is approx 13kW. It will be interesting to see what effect it has.
 
Last edited:
  • Like
Reactions: John.g
Having lived with this problem for nearly two months, I decided it was time to call in a pro. His initial diagnosis was a faulty WB DT10 prog stat - the transmitter was losing contact with the receiver in the boiler. I suggested that this could be checked by moving the transmitter closer to the boiler, which he did. It made no difference! The engineer then decided to check the heat exchanger, so he took the inspection cover off. The hex was blocked almost solid. 10 minutes later, after wielding his special cleaning brush, the channels were clear of muck and cover replaced. Boiler lit - and stayed lit. Water temperature rose to nearly 70C without the boiler off. Room stat did its job. Everything working as it should. 😀

For future reference:
what causes the hex to get blocked?
what is the actual material causing the blocking?
does it mean that the hex will soon need replacement (or a new boiler)?
 