BTU's at delta T65 and T50
View the thread, titled "BTU's at delta T65 and T50" which is posted in UK Plumbers Forums on UK Plumbers Forums.
Hi Guys,
Need some help. I have calculated online the BTUs for the rads (calculator used T65) then when purchasing I was looking at the T65 radiator calculations.....
But I have since noticed, Europe uses T50 as standard. What calculation would I use to convert the T65 BTU needed to the new T50 (I presume I would need to increase the number).
Or would it stay the same and I would just need to choose rad BTU's at T50?
Flow plus return temp
Divide by two
Minus your room temp
Eg
65+50
115/2
57.5
Mins let’s say 18
Gives you a delta t of 39.5
Delta t of 50 you would need your flow and return around 75-65
Which if you have a condensing boiler is bad
TBH I would work off a delta t of 40
Hi Guys,
Output of a 50 deg rad is (50/60)^1.3. I , can't work this out in my present location but very easily done on a spreadsheet . You can also and easier look it up in a radiator temperature correction table.
Hi Guys,
Slightly misread your post so if the calculation was based @ T65 then the correction factor to run @T50 is 1.41, (65/50)^1.3.
IF it had been based @T60 then the correction factor to run @T50 is 1.27, (60/50)^1.3.