Install the app
How to install the app on iOS

Follow along with the video below to see how to install our site as a web app on your home screen.

Note: This feature may not be available in some browsers.

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Jul 5, 2019
1
0
1
Member Type
DIY or Homeowner
Hi Guys,
Need some help. I have calculated online the BTUs for the rads (calculator used T65) then when purchasing I was looking at the T65 radiator calculations.....
But I have since noticed, Europe uses T50 as standard. What calculation would I use to convert the T65 BTU needed to the new T50 (I presume I would need to increase the number).

Or would it stay the same and I would just need to choose rad BTU's at T50?
 
Flow plus return temp

Divide by two

Minus your room temp

Eg

65+50

115/2

57.5

Mins let’s say 18

Gives you a delta t of 39.5

Delta t of 50 you would need your flow and return around 75-65

Which if you have a condensing boiler is bad

TBH I would work off a delta t of 40
 
Hi Guys,
Need some help. I have calculated online the BTUs for the rads (calculator used T65) then when purchasing I was looking at the T65 radiator calculations...
But I have since noticed, Europe uses T50 as standard. What calculation would I use to convert the T65 BTU needed to the new T50 (I presume I would need to increase the number).

Or would it stay the same and I would just need to choose rad BTU's at T50?
Output of a 50 deg rad is (50/60)^1.3. I , can't work this out in my present location but very easily done on a spreadsheet . You can also and easier look it up in a radiator temperature correction table.
 
Hi Guys,
Need some help. I have calculated online the BTUs for the rads (calculator used T65) then when purchasing I was looking at the T65 radiator calculations...
But I have since noticed, Europe uses T50 as standard. What calculation would I use to convert the T65 BTU needed to the new T50 (I presume I would need to increase the number).

Or would it stay the same and I would just need to choose rad BTU's at T50?

Slightly misread your post so if the calculation was based @ T65 then the correction factor to run @T50 is 1.41, (65/50)^1.3.
IF it had been based @T60 then the correction factor to run @T50 is 1.27, (60/50)^1.3.
 

Official Sponsors of Plumbers Talk

Similar plumbing topics

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.