View the thread, titled "Central heating not circulating after New Navien Combi fitted to Santon Premier system." which is posted in Central Heating Forum on UK Plumbers Forums.
Yep
Low loss header
Then if the old boiler was running at ∆T 11°c the pump would of been capable of the higher flow rate and pressure required to overcome index circuit.
Sounds like this needs a low loss header and suitably sized secondary pump. The secondary side pipework will be ok in size but the new boiler internal pump isn't capable.
Alarming really as the installer really should have considered this 🤔
Makes you laugh tho they thought a 15-70 would do 2” pipework it’s the state of the industry atm either people don’t care or they don’t know chances are it was a 25-80 or 32-80
Was he even commercially qualified to work on the install
I agree. The boiler developed a leak from the heat exchanger seal 9 weeks in and charged 200 quid to do a 35
minute job under guarantee. Now they do not want to know.
That would of been a warranty job and the manufacturer liable for payment, not you!
Unfortunately to rectify this is going to cost more and the situation clearly demonstrates the installer doesn't understand the principles.
This customer is prepared to spend money in excess of what was paid for what should have been paid under
warranty in a small claims court.
I think between us we have arrived at the problem. My concern now though is as I mentioned above are the existing rads at ∆T 60°c, if so the flow temperature will need to be around 90°c to give a rad MWT temperature of 80°c and full out put.
yes hat makes sense but I have to get the water around the system in the first place.
You're going to need to separate the system and as Shaun says a plate heat exchanger is your best bet as it will protect the boiler circuit from your decades old and no doubt fouled system. once you separated then a suitable pump will be installed on the flow out of secondary side of the plate heat exchanger.
At this point I strongly urge you to find a firm/engineer who understands the principles of hydronic system design.
Close enough
A pump is required to supply the pressure required and the flow rate required. It's actually the system that creates the pressure but the pump has to be able to meet demand. As it stands the boiler integral pump just can't do this.
Reply to the thread, titled "Central heating not circulating after New Navien Combi fitted to Santon Premier system." which is posted in Central Heating Forum on Plumbers Forums.