Can someone please clarify the regs on ECV's in flats for me as my head hurts 😕
Reading my G1 book, it states that an ECV should be fitted to the installation pipe where it enters the building where the meter is sited 6m or further away from the building.
I have a large block of flats that all have meter boxes doted around the perimeter of the building and lovely yellow gas pipes running up to each flat.
So how do I interpret this 6m away? it states from the building, well the meters are all on the perimeter of the building, so not less than 6m away, but obviously the meter is more than 6m away from the top flats.
Some have ECV's located within the flats with a test point, and others don't.
So is it 6m from premises, 6m from each flat, and if so is it 6m from the front door to the flat or 6m in any direction you like??!!
clear as mud hey 🙂
basically m8 any meter over 6m away from the property has to have a secondary ecv at a point were it enters the building on the inside, i would only interput 6m from ground level flats, and any meter on any other floor on most buildings is further than 6m. so therefore should have ecv on building entry, its all to do with access in emergency so it makes sense if ur a camel ride away. personally i like an emergency control valve even in my house
the "6m rule" is from the meter ECV to the point of entry to the property, so there are plenty of ground floor flats and houses that require an additional ECV depending on the layout of the prop, eg an external meter 4m from the original back door of the prop doesnt need one (like 99% of properties) however if the property gets an extention or conservatory which means the new door is now more than 6m from the ECV it now requires an additional ECV, as said most upstairs flats will require an additional ECV depending on the position of the front door to the ECV, but some have the meter next to the door at the stairs which can be classed as the point of entry
Evening,
clear as mud hey 🙂
i interpret the 6m as a 6m walk not as the crow flies, ie how far do you need to walk from the point of entry of the property to the ECV, you could have meters outside for flats where the 2nd floor flat window is less that 6m vertically from the ECV but is a bit of a stretch to lean out the window to turn it off,
Totaly agree with Kirk on this. Another consideration is, that you nearly always end with a communal meter install. 4 in a row for example. So in an emergency the occupier runs out and turns off the wrong meter because they are not clearly identified or in some cases incorrectly identified. I interpret that if its a multi occupancy building there should be an additional ECV where the gas enters the flat, with a correctly worded label, stating what to do incase of a smell of gas.
just to clarify is a test nipple a requirement aswell and if its not present regardless of the age of the installation its always AR?
why would no test valve be AR? you could do a TT from an appliance inlet point (if it has one) full TT could be done from the meter if required, AECV is to turn off gas in an emergency, test point is only for the gas engineer to work on
hi there what about earth bonding then should be with in 24" of meter or not
depends where the meter is, electricians require the bond to be connected and tested properly they dont care about within 600mm of meter outlet, that is a gas pipework reg not an electrical reg. if it is a remote meter the spark will connect the cable to the first point of access within the equipotential zone (which is usually inside the house)
There should be ECV's fitted inside individual flats where the multiple meter installations are located in a remote or communal area regardless of the 6m rule. The occupants must have a means of isolating gas escape.
With regards to the bonding, the dom gas install shall have the bonding on the pipework as it enters into property side of supply as near as poss, and if present within 600mm of meter before any branch is taken off.
sorry the way i written it didnt make clear what i meant. The second part of my question was referring to the aecv
no AECV is NCS, unless there was a leak then it would be ID, not sure if there are any AR's on no ECV as it is either a gas leak or not
Evening,
clear as mud hey 🙂
where did you train ? able skills in dartord by chance
Reply to the thread, titled "ECV's in flats" which is posted in UK Plumbers Forums on Plumbers Forums.
Blake,
SafeGasInstall,