I did wonder if it makes a difference with the pump on the manufacturers diagram. Being a pump to take the water to the low loss header then taken of this with other pumps for each zone. This installation is just one pump for the system no low loss header.
What is the proposed pump make/model if available and how many zones?
 
I did wonder if it makes a difference with the pump on the manufacturers diagram. Being a pump to take the water to the low loss header then taken of this with other pumps for each zone. This installation is just one pump for the system no low loss header.
 

Attachments

  • Screenshot_20210221-151238.png
  • Screenshot_20210221-151254.png
At 34 rads I was thinking of a 35litre expansion vessel. Was thinking roughly 8 rads for a 8litre vessel on a combi. But due to the high kws of the boiler I take it a 50litre would be better?
 
At 34 rads I was thinking of a 35litre expansion vessel. Was thinking roughly 8 rads for a 8litre vessel on a combi. But due to the high kws of the boiler I take it a 50litre would be better?
Here you go mate go with 50 litre vessel all the best . Kop
 