Expansion position on zoned heating

View the thread, titled "Expansion position on zoned heating" which is posted in UK Plumbers Forums on UK Plumbers Forums.

Just wondering if anyone had any thoughts/ objections to position of expansion vessel. 3 zones on heating upstairs, downstairs and UFH. All zone valves on flow, pump on flow, loss header as well. Expansion vessel it situated on the return from the upstairs zone. I suppose it can’t be cut off by any means
 
As above. Ideally you want the vessel on the return going back to boiler, with the pump shortly after it. This creates a positive pressure through the boiler and system back to thr neutral point where the vessel is tapped in and a short section between vessel and pump under negative pressure. This creates ideal pressure throughout the system as well as not exposing the vessel to high flow temperatures, which lead to early failure of the diaphragm.
With a low loss header you should tap in the vessel on the bottom of the header, this creates the neutral point, with positive pressure through boiler loop.
 