Matt0029

Gas Engineer
Oct 6, 2017
1,245
110
63
37
leeds
Member Type
Heating Engineer (Has GSR)
I have a 35litre central heating expansion vessel that has come with a pre charge of 1.5 bar. Does this sound a little heigh? As the pressure in the system will have to rise above 1.5bar for it or absorb any expansion? Thanks
 
1616398016864.png

1616397932033.png
 
  • Like
Reactions: king of pipes
This is the way its supposed to work.
If the expansion vessel is on the pump suction and near the pump, the pump suction will be at the EV pressure and the pump discharge will be at the EV pressure + the pump head. If the EV is on the pump discharge and near it then the pump discharge will be at the EV pressure and the pump suction will be at the EV pressure - the pump head.
Its recommended the EV is positioned at the pump suction as the whole system will run with a higher average head.

One would think that the pressure should fall by 0.4bar (the pump head) when it stops, can you show a sketch of layout of pump, EV and pressure gauge location?.
Could the expansion stop it falling by 0.4bar when the pump stops? I will do a sketch.
 
Can I also ask what happens to the pressure when the pump kicks in as the gauge drops by 0.4bar (ish).
This would indicate that the EV is on the pump discharge and the PG on the pump suction since it drops in pressure but IMO it should rise again by the same 0.4bar once the pump stops irrespective of the static pressure, hot or cold.
 
This would indicate that the EV is on the pump discharge and the PG on the pump suction since it drops in pressure but IMO it should rise again by the same 0.4bar once the pump stops irrespective of the static pressure, hot or cold.
It doesn't rise again after the pump stops. To does rise after the 0.4bar drop relatively quickly. Just conserned with it dropping on start up that if the system lost abit of pressure. Cold cut the boiler out on start up due to the pressure drop when the pump starts. Thanks.
 
Boilers cut out pressures are normally 0.5/0.6 bar so depending on where the EV and the boiler and pump are located and if the cold filling pressure is 1.0 bar or lower then it possibly could with a cold system, EVs are generally pre pressurized to 1 bar and filled to 1.5 bar so well away from this.
If the boiler has its own pressure gauge watch this on pump start up and see what the actual pressure is. I would assume that if any boiler trips on low pressure that it will annunciate same and have to be reset to enable boiler restart after system top up.
 