Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

View the thread, titled "flue gas analysis" which is posted in Gas Engineers Forum on UK Plumbers Forums.

OFTEC figure I was given is not to allow C0 go above 90, preferred C0 figure to aim for is below 50 on condensing boilers.
 
As far as I know they are using BS 7967 I don't see the actual figure of 90 ppm in the OFTEC manual I remember from the OFTEC course.
 
Just to add something to this.
A maximum 200ppm CO is a limit BG work by.
Worcester also state this limit for their boilers.
 
Hahaha i remember something about 200ppm but cant think where from, dont beat yourself up. im on the case and i'll try to find where i read or heard it from..
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "flue gas analysis" which is posted in Gas Engineers Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread Information

Title
flue gas analysis
Prefix
N/A
Forum
Gas Engineers Forum
Start date
Last reply date
Replies
31

Thread statistics

Created
migoplumber,
Last reply from
Whyme,
Replies
31
Views
1,634

Weekly or Monthly Email Digest

Back
Top