Cables are often oversized. I never use any heavier cable to a boiler than 1.0mm and that is more than plenty.
Fuses are for protecting cable to appliance and, perhaps slightly less importantly, the appliance itself.
 
T&E cable from a spur to a boiler is fine, providing you use a wiring box, or another spur to take white 3 core round cable into boiler
 
So have you taken 1.5t&e into the boiler

I havent done anything, this is just one ive came across that has got me thinking. But yes t+e into boiler. Mi's say at least 0.75mm pvc insulated cable....dosent say you have to use flex.
 
To throw a spanner the works, you could feed an FCU with a run of 1.5mm t+e clipped direct from the consumer unit and protect it with a 16A 60898.
 
I havent done anything, this is just one ive came across that has got me thinking. But yes t+e into boiler. Mi's say at least 0.75mm pvc insulated cable....dosent say you have to use flex.

dude it sounds like your out of your depth, from the fused spur to the boiler use flex looks much better and you wont have any problems with the glands on the boiler
 
Last edited:
I havent done anything, this is just one ive came across that has got me thinking. But yes t+e into boiler. Mi's say at least 0.75mm pvc insulated cable....dosent say you have to use flex.
That's because they don't make 0.75mm flat t&e
 
or if you got a bit of 1mm pyro knocking about you could use that as well, might be a struggle to make off for most folks though ;-)
 
or if you got a bit of 1mm pyro knocking about you could use that as well, might be a struggle to make off for most folks though ;-)

not if you still have the potting tools 😀
 
That was why I asked the question. 2.5mm from the board on a 15amp 3036 rewireable fuse to the immersion. Then a 1.5mm from the spur to the boiler with a 3 amp fuse at the spur. Just thought the 15amp at the board should be changed to a 6amp. Wasn't sure with the 2.5mm t+e.

You can't spur off a radial circuit!
 
Flex is used because of the fact the front control panel is made to move for access, flat t&e is used for fixed wiring, and I can't remember pyro being used for anything that could move.
 