Guest viewing is limited

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Gledhill boilermate BMSCP180

View the thread, titled "Gledhill boilermate BMSCP180" which is posted in Boiler Advice Forum on UK Plumbers Forums.

lordyjordy111

Gas Engineer
evening

I recently took out a boiler mate 2000 and replaced with a boilermate BMSCP180.

Straight swap all pipe sizes the same. The customer is complaining that there is a loud vibration noise of a night when only the hot water is on.
its a worcester so i think its when pump overun is running.

Ive played about with the by pass. trying it on 2 up to 6. she still has the isssue.

I did not put a balancing valve on hot water so Ive throttled back the pump valve for a few days in case its the speeed of the water (on hot water. its a big house needs to be on 3 for rads) still has the issue

I have visited the property but cant make it make the noise. I dont think its a stay on the coil as i have set by pass on 6 and shut heating and hot water at the same time when hot. no noise????

any ideas. thanks in advance
 
I’ve had a brief look on the instructions, so you say you’ve omitted the charge control valve?
 
Guys apologies for not coming back to you on this one. Btw I put a modulating pump in and it fixed it. I had a ups2 on there on speed 3. Put a ups3 on there on modulating and no more noise.

Cheers guys
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Gledhill boilermate BMSCP180" which is posted in Boiler Advice Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
lordyjordy111,
Last reply from
lordyjordy111,
Replies
3
Views
1,508
Back
Top