I have a 2 year old glow worm boiler which was installed in new build home. At the side of my house there is a plastic vent from the boiler and then further along the wall say 2 metres there is a copper pipe. A few months ago I noticed the pipe had a steady drip and the ground underneath was wet. The drip seems to have got quicker in the last week or so. I have looked online and people say there should be a plastic condenser pipe which can drop - I can't see a plastic pipe only the vent. They also say it could be pressure relief pipe. I have checked the boiler pressure and that reads between one and two bar. I don't really want to get an engineer out if this is something that should happen or it's something I can fix easily. Any help appreciated
 
Hi thanks got coming back so quickly.
Pictures as requested.

Img 23 and 24 are underneath boiler. 25 is the whole system. 26 is the dripping pipe which is to right of back door. 27 is another copper pipe i spotted which appears to be directly under 28 which is the boiler vent. I now wondered if the dripping pipe is the toilet overflow as bathroom is directly above. Not sure how to tell though and didn't think that pipe would be copper. However the toilet sometimes does not stop its self refilling after a flush and you have to refresh to stop the water flowing into bowl.

IMG_0023.jpgIMG_0024.jpgIMG_0025.jpgIMG_0026.jpgIMG_0027.jpgIMG_0028.jpg
 
That pipe looks like the safety relief from the heating!? Which would lead to a drop in pressure... Although the black handle looks like its been left in the open position so maybe it's creeping past & topping pressure up :/
 
  • Like
Reactions: 3 people
Could well be overflow from unvented cyclinder which is in airing cupboard and would be directly above where the pipe is
 
Could well be overflow from unvented cyclinder which is in airing cupboard and would be directly above where the pipe is

1. Unvented cylinders don't have an overflow.
2. Look at the mortar joint, an unvented discharge will be 22mm at minimum, that looks to be 15mm so it has to be the heating safety discharge.
 
  • Like
Reactions: 2 people
The copper pipe with the dodgy soldering is 20mm diameter. That's the one that's dripping
 
its had a exp valve done, i would be inspecting if that works ok too!

comisserations on the installed boiler though.
 