Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Grant Vortex Condensing Boiler air in fuel?

View the thread, titled "Grant Vortex Condensing Boiler air in fuel?" which is posted in Boiler Advice Forum on UK Plumbers Forums.

hi
I have a grant oil fired boiler that is approx 4 years old. Recently the burner has started locking out. If I press the reset button it will start and fire and heat enough water for a shower etc... but then locks out. Sometimes it will stay on for a couple of days and give hot water on demand but will then lock out again. This was serviced around 6 months ago and a new nozzle was fitted and a new filter at the discharge point of the tank. Is the ‘steam’ colour any indication of what is happening? When this was operating perfectly this was white but now sometimes it white but other times when running is is almost colourless. I am guessing not getting to high enough temperature. I have tried to bleed fuel a few times and each time it seems to bubble and ‘fizz’ a bit. Is air getting in? There are compression fittings at tank (filter), fire valve and at 90 degrees just after fire valve where it comes through the wall
Thanks
 
Could be air getting drawn in, but best get your service guy back out to check it all and make sure all joints are replaced or repaired that might be not sound.
Does it have a one or a two pipe oil line, or a Tigerloop device?
 
Thanks. Just one pipe supply. I did have the guy back last week but he wanted to strip down the boiler, dig up the oil pipe outside etc... and he couldn’t do it for at least 2 weeks but I think it could be more simple than that. I have just checked the pipe outside and think there is a trace of kerosene there so if oil is coming out could air be getting in?
 
Yes it is possible for air to be drawn in if you are noticing a trace of kerosine.
But a good oil engineer could test for that easily and probably have vacuum gauge for checking.
 
Pressure test the oil line to find your leak. I suspect it will be badly done joints (probably compression fittings without the required brass inserts in the ends of the pipes) allowing air in. Sounds like your guy is just guessing
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Grant Vortex Condensing Boiler air in fuel?" which is posted in Boiler Advice Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
Jambo1967,
Last reply from
WHPES,
Replies
6
Views
1,875
Back
Top