Pump is on 2 as the system is quite large 12 rads.What speed is the pump on now?
Cheers.
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Pump is on 2 as the system is quite large 12 rads.What speed is the pump on now?
Pump is on 2 as the system is quite large 12 rads.
Cheers.
I
If it works well it's fine. You want them on the lowest setting that works and gives the right flow and return temps.
With the valve:-
screw it shut, turn on the heating and hot water so both Motorised valves are open and the pipes start to get hot. Slowly open the Auto by-pass 1/4 turn at a time, (a few seconds in between turning), until you feel hot water flow through the by-pass. Then close it back around a half turn.
That's the best explanation I can give on a Forum. I would be going to greater lengths to set things up and balance the system if I were doing this in person but it will do!
Please do come back and tell us how you went on.Thanks I'll do it on Saturday and let you know how it goes.
Cheers.
Hi.Please do come back and tell us how you went on.
Does the light on the pump flash or stay solid?
Okay. That's fine. If you were running it in flashing mode, then it would not be running fixed-speed, and the automatic bypass valve wouldn't be able to work as it should.
When you say restrict the flow on hot water,is this when the system is running eg demand from heating/hot water? The hot water coil should have a balancing valve on it that should be restricted (which from the pic you have one after the 2port) to stop the heat just whizzing around the coil and giving less to heating
It should be restricted yes,but are you only getting flow through the by-pass valve when there is still demand for ch or hot water an your closing the balancing valve?
Photo attached. Cheers.What size of pump is it, I can't read it
You don't really want water passing through the bypass when the valves are open so I wouldn't worry too much about that if the flow and return temps are ok at the Boiler.
I'm surprised it still bangs but you do need to rule things out like the lack of a by-pass before you can start to think of other possibilities,
I'll put my thinkin cap back on.