Hi,

My oil boiler has just locked out, pressed the reset button on the burner and it doesn't light and just locks out again after a minute.

It has plenty of oil and has never run out.

Tried calling an oftec engineer and no one can come for a week, I repair lots of gas boilers but not experienced with oil.
 
Do you know what burner it has?
When you say doesn’t relight does the motor run and goes through pre purge/start sequence?
 
Could be capacitor, seized pump or bearings seized. Check capacitance on capacitor, any less than 70% original value I was told to change. Isolate fuel, take pump off and see if shaft spins freely, could be seized or have tight spot. While pump is off check electric motor shaft is free spinning.
 
Before you start taking off oil pumps and the like, lift the air cover on the end of the motor and see if you can move the fan, if not something is seized and needs further investigation, if the fan moves then its probably the motor capacitor gone west.
 
If the motor is spinning freely and no tight spots and had feed to motor and the cap is replaced like for like ie. right uF value then like best says it’s probably the motor, windings burnt out? If you replace motor check data plate on it to get right model and wattage
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Heatslave 20/25 lockout" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
markadams,
Last reply from
Peter J Brown,
Replies
11
Views
8,794
Back
Top