Hi

Iv been called out to an oil boiler breakdown found the fault (fuel pump) Iv fitted a new fuel pump and got the boiler running again I checked the existing nozzle and found it was a 35sec nozzle I fitted another nozzle today but can't get anywhere near with the co2 reading the boiler is a 1980s heatmaster boiler the company is now bust with a selectos d42/a burner any help on correct nozzle size would be great Iv fitted a 0.50/60r with the pressure set at 140psi as this is the only information I can find.

Martin
 
I still have some detailed info on the D42 Selectos burners, but not specific to that boiler.
If that burner has the adjustable blast tube diffuser, then that will add to the complexity of setting it up.
If it has the fixed one piece blast tube/diffuser, then should be straight forward using an analyser.
Dont worry if CO2 isn't much above 10%
 
Last edited:
What is the output of the boiler?
What size nozzle did you remove?
Is it running on class C2 or class D oil?
Have you cleaned and made sure all the baffles are in good condition and in the right sequence?

There are still a huge amount still running class D (35sec) fuel.
 
Hi it was fitted with a 35sec class d nozzle but is running on class c. Iv cleaned all the baffles and they back in right sequence. Not sure on the output as there is no information on the boiler.
 
One issue could be you have changed the flame angle from 80* to a 60*. The burner was used for boilers in excess of 20kw. Swap the nozzle for a 0.8/80s set the pump to 140psi. Set the air intake at approx 1/3rd open then test.

None of the old manuals I have got list a nozzle smaller then that for this burner.
 
I have an original Selectos burner instructions for a D42, which is 40 plus years old. But there are newer models also with adjustable flame ring.
The flame ring (diffuser, as I call it) distance away from front of blast tube is - Flush for up to .75 nozzles, then 1/16" out for .85 up to 1.0 nozzles.
The pump pressure for Kerosine on Thorn ODY boilers was 100psi for .65, 80 degree AR nozzle with a CO2 of 10%.
You probably need a S nozzle of 80 degrees.
 
Last edited:
  • Like
Reactions: 1 person
Right guys and update i have fitted another nozzle today 0.65\80 s turned the pressure down to 100psi the ppm reading have dropped but there still high around 600ppm the co2 was around 7.8% i have cleaned the boiler baffle ect but still can't get the ppm down to where i would like. Do yo think its worth running the boiler for a couple of hours and retaking a sample?

Martin
 
Have you checked the flue for obstructions?

Has any oil dribbled into the combustion chamber, or has any soot got into it?
 
Last edited:
Is it a balanced flue model? If so, the seals between the air inlet and discharge may have broken down allowing combustion gasses into the air intake.

If not, try changing the position of the flame spreader in relation to the nozzle.

Your problem will probably be something to do with air

Also check fuel is not leaking from behind the nozzle. Sometimes the nozzle holder can be worn with repeated taking nozzles in and out, A couple of turns of PTFE round the nozzle thread will fix this.
 
Last edited: