Hi

Can you help me determine if my new Navien lcb700 lsx is working as expected?

I got the Navien oil boiler installed to replaced an old firebird boiler. The new boiler is a condensing oil boiler and I’m not sure if this is working as expected. I’ve a 300 L water cylinder and after one hour of heating the water temperature reaches 40-45C. The cylinder is less than a year old and the thermostat is working well.

When the heat demand is on, the boiler themostat is set to 60C. The burner starts and the boiler lcd panel reaches 60C. The burner will stop and the pump continues to run. When the temperature at the boiler drops to 40C, then the boiler will burn again to 60C. The cycle continues and the 60C to 40C drop takes about 20 minutes.

My question for anyone….is this normal?

Thanks
 
Unvented cylinder?
Hi thanks

I somehow struggle to understand the difference. It’s a cylinder that is fed by a water tank in the attic, so I think it’s unvented. It’s a joule wellmaster 300L, controlled by a heatmister system and a 2 port valve.

Thanks for your help.
 
As the coil on the cylinder is 22kw yes you will have some cycling also with the cylinder temp increasing this will also increase cycling/ time before it fires the boiler again
 
As the coil on the cylinder is 22kw yes you will have some cycling also with the cylinder temp increasing this will also increase cycling/ time before it fires the boiler again
Hi
Am I incorrect to expect the boiler to continue to fire until the water in the cylinder has reached the thermostat set temperature?
 
Hi
Am I incorrect to expect the boiler to continue to fire until the water in the cylinder has reached the thermostat set temperature?

Yes or until the boiler is upto temp then it will wait until the temp drops below its threshold then refire and repeat
 
It will be around an hour due to the coil being miss matched
Hi
Cheers
My boiler won’t heat the temperature in the cyclinder from 30 to 60 within an hour. In fact, it won’t even manage this is 90 minutes.

Can you think of any reasons for this? It’s the only zone on at the time.
 
Yea something isn’t right any chance of a picture of the airing cupboard?
 
Hi

Yes, my airing cupboard with my cylinder and the heatmister control area.

The 90 won’t heat the water when it is the only active zone.

Thanks
 

Attachments

  • IMG_2200.png
  • IMG_2199.png
There’s a red wheel headed valve above the ufh stuff is that open fully ?

You coil is big enough now due to you having a twin coil system in series
 
Could be supply pipes from the boiler not fully clear / restriction as I would say that coil would easy heat the cylinder up within the hour
You might be right. The last boiler used 28mm pipe and this uses 22mm supply/return but connecting to the existing 28mm pipe into the house
 