Hi guys,
ventilation is not my strong point so bear with me and would rather ask about it than get myself in the shoite.
Just been to a first floor flat which has had its warm air boiler shut off by transco due to the apparant lack of ventilation for the appliance.
The boiler is situated in a hall probably 3m long and has a lounge, a kitchen with an air brick (albeit covered by the washing machine),a bathroom with a vent direct to out side air and the front door which leads onto a landing in the communal area with a front and back door off it (very drafty).
None of the doors have any ventilation and the appliance has a heat input of 10.8kw.
I need help with getting the correct ventilation for the appliance and which doors i would need to put the vents in or whether i would need to put vents in all of the doors.
Any help would be appreciated. cheers.
after just reading through my viper book i have seen that i am able to take the path of ventilation through the bathroom because the appliances heat input does not exceed 12.7kw, so..
i need 5cm per kw over 7kw so therefore i would need a vent providing at least 20cm of ventilation??
can someone please confirm this for me.
ventilation is not my strong point so bear with me and would rather ask about it than get myself in the shoite.
Just been to a first floor flat which has had its warm air boiler shut off by transco due to the apparant lack of ventilation for the appliance.
The boiler is situated in a hall probably 3m long and has a lounge, a kitchen with an air brick (albeit covered by the washing machine),a bathroom with a vent direct to out side air and the front door which leads onto a landing in the communal area with a front and back door off it (very drafty).
None of the doors have any ventilation and the appliance has a heat input of 10.8kw.
I need help with getting the correct ventilation for the appliance and which doors i would need to put the vents in or whether i would need to put vents in all of the doors.
Any help would be appreciated. cheers.
after just reading through my viper book i have seen that i am able to take the path of ventilation through the bathroom because the appliances heat input does not exceed 12.7kw, so..
i need 5cm per kw over 7kw so therefore i would need a vent providing at least 20cm of ventilation??
can someone please confirm this for me.