Went to do a service today on above boiler. Ration was 0.0021 and ppm was 222. Co2 was at 10.3 which is within the limits stated. This is AR then hey?

It also had a burst expansion vessel and is under warranty so turned boiler off and told them to call Manufacturers in to fix.
 
Yes, all other limits were ok. I thought i was told if ratio is out (not according to mi's)it was at risk?

If it is out adjust it back in. It is quicker than writing out a bit paper. They drift out a bit over time.
10.3 is ok on a greenstar (9.8 + or - 0.5).
 
  • Like
Reactions: 4 people
Wow u actually pay attention to the numbers I just bang it in sample port, if the 300 ppm warning don't go off I'm back on silver and off to my next 59.99 service.
 
  • Like
Reactions: 4 people
the co2 is what you want to watch on WB's tbh.

the manufacturer's engineer will probably test gas pressures and fga readings when he/she attends anyway.
 
Greenstar, on service mode low 9.2 High 9.8 +/-2 %

max co 200ppm, a little adjustment normally reqd after a couple of years.

In the past, silly readings have been faulty meter governor.
 
  • Like
Reactions: 2 people
Tweak the co2 down to 9.8 and the ppm will drop accordingly I bet...
 
Thanks chaps. Next time I will adjust the valve to getter better readings. To be honest, I would have called WB up but as they were coming out the next morning due to burst expansion vessel I thought I would let them do it. Whe I was on the baxi course I learnt that if a vessel has burst and you cannot get hokd of obe, then just empty half a rad with lock shields on until you can come back. Do you guys do this? Or just tell custard not to use it
 