Who said anything about squeezing water through pipe? The purpose of balancing is to get the correct flow through every radiator. The fact that each radiator is fed by a separate pipe helps but a 500W rad still needs half the flow rate of a 1kW rad.
I doubt if Drayton and Honeywell would agree with you.
Water has roughly 1.163 Wh/kg/K and 1kg/l.
At DeltaT 10K that is 11.63 Wh/l.
That gives you 43 l/h.
DN6 has 0.028 l/m. Resulting in 0.42 m/s.
But to KISS it: 500W / (11Wh/l *3600) = 0.0126 l/s.
My flow resistance table goes up to 0.025 kg/s for DN6.
Meaning your comparably tiny rad of 6x6 K2 will result in > 0.566 m head per meter.
At a 5m distance from your manifold this is > 5.66m head.
Or in other words, to use this radiator as per design it needs a separate Alpha2L 15/50 for itself.
I am not saying it does not get heat as the resistance per meter drops quickly. Are you sure that Drayton and Honeywell will tell me that physics are not valid for plumbers?
As for the balancing I have to apologise. Grundfos Ecademy does not provide these courses for UK.