This heating system is new to me, in reality about 8 years old and in good condition.
In the tail end of last winter's heating season, I think I shot myself in the foot. With more bedrooms than occupants and a water cost of about £4/tonne,
I had a water meter installed.
It might have been a coincidence, but within days I discovered the boiler was leaking. To be specific the gasket had blown on the valve on the top of the boiler, where the boiler decides to prioritise the hot water over the heating the unit, when (say) running a bath.
I had not realised that the water meter would include a non-return valve, so prior to that installation the expansion of the hot water would simply have passed a small quantity back into the rising main.
Poking through the back of one of the kitchen cabinets, there is something that could be an upturned egg cup suitable for a swan's egg, perhaps a bit smaller than a British standard handfull.
Perhaps this corner cabinet was fitted after the boiler because now I cannot get my shoulders into the cabinet and this thing should be pressure corrected every 6 months. [The air was blue as the plumber and I tried to achieve the required pressure AND then remove the air pump, without its internal bladder going flat again. the plumber was muttering that normally there is enough pipework to absorb changes in pressure, but my hot water is all back to back on the ground floor so minimal in length.].
It seems the way out is to fit another expansion vessel on (say) the bathroom hot pipe where it would be a one-man job to check the pressure?.
Is this a sensible idea and is any particular make recommended?
In the tail end of last winter's heating season, I think I shot myself in the foot. With more bedrooms than occupants and a water cost of about £4/tonne,
I had a water meter installed.
It might have been a coincidence, but within days I discovered the boiler was leaking. To be specific the gasket had blown on the valve on the top of the boiler, where the boiler decides to prioritise the hot water over the heating the unit, when (say) running a bath.
I had not realised that the water meter would include a non-return valve, so prior to that installation the expansion of the hot water would simply have passed a small quantity back into the rising main.
Poking through the back of one of the kitchen cabinets, there is something that could be an upturned egg cup suitable for a swan's egg, perhaps a bit smaller than a British standard handfull.
Perhaps this corner cabinet was fitted after the boiler because now I cannot get my shoulders into the cabinet and this thing should be pressure corrected every 6 months. [The air was blue as the plumber and I tried to achieve the required pressure AND then remove the air pump, without its internal bladder going flat again. the plumber was muttering that normally there is enough pipework to absorb changes in pressure, but my hot water is all back to back on the ground floor so minimal in length.].
It seems the way out is to fit another expansion vessel on (say) the bathroom hot pipe where it would be a one-man job to check the pressure?.
Is this a sensible idea and is any particular make recommended?