I work for a gas transport company as a FCO, been out to a SOG at meter and initial tightness test produced 11mb drop. I sniffed it out to a joint and sprayed with LDF which produced some spawn but then stopped.

Second tightness held completely and failed to pick any readings from the same joint.

Has anyone heard of LDF masking such a large leak because it’s the first time for me
 
Where was the reading in relation to the ECV? More likely to be intermittent escape on ECV. (opening and closing redistributes grease)

No checked ecv, it was definitely that jount. Left it to dry out and 47 LEL reading. Third test 11 mb drop.

Ecv leak won't show on TT anyway think about it.

I just not experienced anything like it
 
No checked ecv, it was definitely that jount. Left it to dry out and 47 LEL reading. Third test 11 mb drop.

Ecv leak won't show on TT anyway think about it.

I just not experienced anything like it
,

Yes, it can. On an old tap, and depending on the distribution of grease at that particular time.
 
  • Useful
Reactions: 1 person
I work for a gas transport company as a FCO, been out to a SOG at meter and initial tightness test produced 11mb drop. I sniffed it out to a joint and sprayed with LDF which produced some spawn but then stopped.

Second tightness held completely and failed to pick any readings from the same joint.

Has anyone heard of LDF masking such a large leak because it’s the first time for me

Thought about it for a while, I knew an engineer who had a massive drop. He sprayed every visible joint using a cheaper ldf. He called another engineer who had a more expensive brand, and found it on one of the joints he’d already sprayed, a hairline crack on an elbow.
 
It was a poorly made joint, and LDF was enough to stop it .

It goes to show the limitations of the tightness test and on low pressure gas.

Thankfully we are given test equipment that is able to find these things.
 