Just finished commissioning the Vaillant boiler. Pressure slightly low at 2.76 m3/h. 30kW. Old boiler was a 24kW.
Tested the hob and all burners go out on simmer. Owners reckon this is a new thing.
Only hob and boiler on gas.
Pipework from meter is 22mm, goes in house and under floor in 22mm approx 3-3.5m. Comes out of floor where boiler is in 15mm.
Standing pressure 24mbar
Working pressure 21.5mbar
Undersized pipework I'm thinking.
Right or wrong??