Nope your looking at the tables wrong. That 2.9m3 refers to a 3m length of 15mm with a 1mb drop.
A mere 20 cm section would flow alot more than that...by my loose reckoning easily in excess of 5m3

I wasn't looking at a table. I was using the mr combi pipe size app and for the length of 15 I have with 1 elbow you won't get higher, needs to be 22

ceeca4987ac4bf7f57e40853133693df.jpg


9410c5b79e6e2a1fdacbd3cefb2fa479.jpg
 
Last edited:
Why not put a reducer on the connection from the boiler and take it straight to 22 or 28? That's what I do with boilers which have 15mm connections. I would also tee the hob off either the 22 or 28mm pipe.
 
  • Like
Reactions: 1 person
App. and Tables in agreement 2.9 flow gives 3 meters and 20 meters for 15 &22.
Length 700mm pressure drop 700/3000 & 700/20000 which equates to the 0.233 & 0.035 given by App.
Phil also right with flow through 700mm length of 15mm. 1/4 of 3 meter length could be expected to give double the 3 meter flow, ( L X Q X Q approx constant).
 
  • Like
Reactions: 1 person
App. and Tables in agreement 2.9 flow gives 3 meters and 20 meters for 15 &22.
Length 700mm pressure drop 700/3000 & 700/20000 which equates to the 0.233 & 0.035 given by App.
Phil also right with flow through 700mm length of 15mm. 1/4 of 3 meter length could be expected to give double the 3 meter flow, ( L X Q X Q approx constant).

Why does the app say for 2.91 with an effective length of 700mm you need 22?
 
Why not put a reducer on the connection from the boiler and take it straight to 22 or 28? That's what I do with boilers which have 15mm connections. I would also tee the hob off either the 22 or 28mm pipe.

I will do from now on! But from what Phil and Joni say I should get enough flow from that short run of 15 ... so what gives?
 
Sorry if you have answered this before, but what is the working pressure at the meter?
 
I dont use apps or rather put an over reliance on them. Pen and paper is best. But ive downloaded one that says different anyway which is more in line with my ready reckoning.

And 30kw is 30kw wether its vaillant, ideal or heatline - its not the boiler. As this demonstrates that small bit of run can handle upto a theoretical 45 ish kilowat

Edit.
Yep accurate drawing of the run.


88eb41eeaf34feb9215e52b32e81ca7a.jpg
 
Last edited by a moderator:
I dont use apps or rather put an over reliance on them. Pen and paper is best. But ive downloaded one that says different anyway which is more in line with my ready reckoning.

And 30kw is 30kw wether its vaillant, ideal or heatline - its not the boiler. As this demonstrates that small bit of run can handle upto a theoretical 45 ish kilowat

Edit.
Yep accurate drawing of the run.


88eb41eeaf34feb9215e52b32e81ca7a.jpg

What app is that Phil?

Agreed re: heat input ratings.. I've tried drawing it and my drawings are confusing.. but basically there are 24 elbows, 2 45s and approx 14 meters of 28mm.
 
Very experienced Gas Engineer was perplexed to be reading 16 at meter with his brand new certified digital manometer. Explanation, it was set for mmHg instead of mbar. Trust nothing at first sight.
 
Very experienced Gas Engineer was perplexed to be reading 16 at meter with his brand new certified digital manometer. Explanation, it was set for mmHg instead of mbar. Trust nothing at first sight.

Lol oh dear!! I used a manual wet u-gauge though
 
I cant put that into a visual way.

But all id say is if youve teed off the 15mm to the hob - I wouldn't have done that. Id have teed off the 28 to the hob and left that final 15mm run to the boiler unimpinged.
 
  • Like
Reactions: 1 person
I cant put that into a visual way.

But all id say is if youve teed off the 15mm to the hob - I wouldn't have done that. Id have teed off the 28 to the hob and left that final 15mm run to the boiler unimpinged.

I hear you about the hob. If need be I'll change it. But even with the hob disconnected from the supply it didn't change the readings I got for the boiler.
 
Was the 21.5 at the meter with the boiler on max or just with the hob on.
And as everyone elce is saying dont have the hob and boiler both of the same section of 15mm pipe.
 
Was the 21.5 at the meter with the boiler on max or just with the hob on?
And as everyone elce is saying dont have the hob and boiler both of the same section of 15mm pipe.
 
So, upped the pipework to 28 in basement, cut in a test point under the boiler and proved pipework was fine at 1mb drop.. still getting 12 working at meter. So I call NG. Guy says, don't run boiler on max rate, just run it normally because we don't test in max rate. Says if he gets good wp at meter at normal rate he's leaving. So I start to call gas safe register. He says run the boiler on max rate. He then finally accepts there's a problem with service pipework and calls it in!!!!!!

He reckons by running a boiler on max rate will generally always get lower than 19 wp at meter. Really? I say. I've never seen this before at the meter when I've done installs. Reckons that's how it is.

Jesus H Christ!!!!
 
  • Like
Reactions: 1 person
They do that with the huge output domestic boilers the manufacturers are selling now.
40kw combi,s, why?
 
Ok.. so back to the original job on this post..

I fitted a Vaillant 30kW system boiler and upped the pipework in 28mm from meter to boiler as boiler and hob wasn't getting enough gas

I've now added a test point to both boiler and hob. I've also teed the hob off the 28 which I brought further up underneath the boiler..

I added the test point on the 15mm.. so!

Standing @ meter 25mb
WP @ meter both app 21mb
WP @ meter 1 app 21.5mb
WP @ boiler test point 20mb
WP @ hob test point 20mb
WP @ boiler with hob on 19mb
WP @ hob with boiler on 19mb

Have told custard to replace hob as burners went out with just hob on- hob is 30 years old.

I expected to see a working pressure of 20 at both appliances when both on.

Pipework is not undersized.

Why am I only getting 19????

30066a0e763dc97d7fbb644b66373427.jpg


3ad66e255d22823d94e68acce94f49c3.jpg


These are my pipe calculations for what's currently there..

a463a0994b3335f88d0b4da92d9ef3cb.jpg


df91809d21cad3a3735cd921b67156b3.jpg
 
Last edited:
1.5 mbar with one appliance running and much better than before

And I'm sure your loosing .5 mbar on that 15mm

One thing I did notice that I haven't seen before, all the readings pulsated on the gauge.. half a bar. Just went up and down constantly by half a bar.. dodgy regulator? Or is that normal?
 
One thing I did notice that I haven't seen before, all the readings pulsated on the gauge.. half a bar. Just went up and down constantly by half a bar.. dodgy regulator? Or is that normal?

Could be but its normal for it to move up and down a wee bit around .5 I would say is normal

Without seeing it it's a guess what do you think ? Are you happy with the results?
 
Could be but its normal for it to move up and down a wee bit around .5 I would say is normal

Without seeing it it's a guess what do you think ? Are you happy with the results?

I'm happy that they're better, but not happy I'm getting a 2mb drop across pipework. But then, I'm not as experienced as you so if you say it's ok I'll go with that and put in a new hob, long as the flame pic and simmer are good I can call it a day..
 
I'm happy that they're better, but not happy I'm getting a 2mb drop across pipework. But then, I'm not as experienced as you so if you say it's ok I'll go with that and put in a new hob, long as the flame pic and simmer are good I can call it a day..

Yea you can double check by phoning your friends up at Nat grid about the reg 😀

Do you know age of reg / what meter is in imperial or metric ?
 