Because it forced combustion (fan driven). I wouldn't be too hasty with the loss across installation as 2mb from meter to gas valve test point is permitted (potential 1.5mb loss from appliance iso to gasvalve if I'm not mistaken). Almost certainly undersized service pipework probably been inserted with serviflex, they use 16mm most of the time and it's way too small. When you next bump into a NG engineer ask for an ecv test point. It allows you to take a working pressure before the regulator and proves beyond doubt what the issue is. Last time I spoke with the grid they said as far as they go is turning a tap on or turning on a room stat if not a combi, they dont put appliances in forced max rate. Hope this helps.
He didn't have any ecv test points :/ supply pipe is inch an quarter. He tested next door and they have no issues.
He said NG will not bother with low pressure calls unless pipework to appliances are correct. So will have to do a new 28mm run and retest, if same issue they'll have to sort the issue out themselves.
I'm surprised they put a 9m 22mm run to a 40kw boiler though
How you getting on jay ?
NG said nothing they can do until the pipework to boiler is corrected. Service pipework is 1.25 inch. He put on a new meter and tested but same issue. Gotta do a 28mm run and retest. If same issue they'll then put in a low pressure callout.
Said that undersized pipework can sometimes cause a low working pressure at meter.
NG said nothing they can do until the pipework to boiler is corrected. Service pipework is 1.25 inch. He put on a new meter and tested but same issue. Gotta do a 28mm run and retest. If same issue they'll then put in a low pressure callout.
Said that undersized pipework can sometimes cause a low working pressure at meter.
NG said nothing they can do until the pipework to boiler is corrected. Service pipework is 1.25 inch. He put on a new meter and tested but same issue. Gotta do a 28mm run and retest. If same issue they'll then put in a low pressure callout.
Said that undersized pipework can sometimes cause a low working pressure at meter.
one way to solve it wheres meter located?
In basement, below the boiler on ground floor
That's utter bollox telk them to sort there side out first working pressure of 10mbar and under isn't acceptable and doesn't matter what size output pipe is still be the same
Cut in test point under boiler, 2 x gauges if it's 9 at test point and 10 at meter your pipes fine.
Have they done a mains upgrade and shoved plastic up the old service?
Discon flexi at ecv and let it blow maybe water in mains?
So call them out again??? :/ thing is, he said NG won't put it forward as a low pressure callout if the pipework is undersized. Hate being the new boy sometimes, now I'm gonna loook like a right idiot to my customer 🙁
give me tonight have a mate who works for national grid, will see what he says
Sounds about right including gas valve test point press drop but even if pipework was undersized you should still get a working pressure at the meter within spec regardless Jay.10mbar meter
8 mbar boiler
so not a million miles out