akingpage
I have had a bit of conflicting information on this, so far i have been told by several commercial engineers that seen as though I am able to run 35mm copper on my domestic ticket I can do the pipework myself as they are going to run the 60 meters from the u6 meter in 32 steel in any case?
I spoke to Gas safe and they have said that I can do the pipework run but the gas volumes would be too big for me to work on with my ticket so I will need a commercial engineer to purge the system, I was reading the trusty "essential gas safety" corgi book and it says that if I isolated the pipework at 0.035m³ intervals then I can purge each section and tightness test each section one by one ensuring I stay inside the domestic volumes for tightness testing?
How can I run the pipework myself if the maximum length of 35mm pipe I can run is 30 meters (insuring I stay within my 1mb differential pressure drop) my working out is just an example:
[Power]-[Flow rate ]-[Assumed diameter]-[Measured length]-[Effective length]-[Maximum length]-[Pressure drop]
[27kw]--[2.52m3/hr]------[35mm]-----------[30 meters]------[30 meters]--------[30 meter]-------[1mb]------
This working out tells me I cant install anything over 30 meters in length on a u6 meter because my pressure drop would exceed 1mb? (right or wrong?)
My questions are:
If I cant run the whole 60 meter in 35mm (due to potentially exceeding my 1mb pressure drop) how can a commercial engineer run the 60 meters in 32mm steel and stay within the 1mb pressure drop on a u6 meter?
Any help will be appreciated
I spoke to Gas safe and they have said that I can do the pipework run but the gas volumes would be too big for me to work on with my ticket so I will need a commercial engineer to purge the system, I was reading the trusty "essential gas safety" corgi book and it says that if I isolated the pipework at 0.035m³ intervals then I can purge each section and tightness test each section one by one ensuring I stay inside the domestic volumes for tightness testing?
How can I run the pipework myself if the maximum length of 35mm pipe I can run is 30 meters (insuring I stay within my 1mb differential pressure drop) my working out is just an example:
[Power]-[Flow rate ]-[Assumed diameter]-[Measured length]-[Effective length]-[Maximum length]-[Pressure drop]
[27kw]--[2.52m3/hr]------[35mm]-----------[30 meters]------[30 meters]--------[30 meter]-------[1mb]------
This working out tells me I cant install anything over 30 meters in length on a u6 meter because my pressure drop would exceed 1mb? (right or wrong?)
My questions are:
If I cant run the whole 60 meter in 35mm (due to potentially exceeding my 1mb pressure drop) how can a commercial engineer run the 60 meters in 32mm steel and stay within the 1mb pressure drop on a u6 meter?
Any help will be appreciated