Evening all. Thanks in advance.

I've had a new Valliant 831 installed at my property but I'm not convinced the upstairs flow and return pipes are sufficient for the number of drops and radiators. I've attached two diagrams, one showing the current layout and another showing my proposed layout. In both diagrams the red lines are flow and blue return, bolder lines are 22mm pipes and the thinner are 15mm. Hopefully the diagrams are useful.

The property used to have a back boiler in the living room which I've marked as drop 2 hence the 22mm pipes that go upstairs from those radiators. Drop 1 now has 3 radiators, it used to have a single radiator.

Before the new boiler was installed I replaced all the radiators with bigger doubles and installed some new ones in rooms that didn't have them. Due to installing bigger radiators I replaced the flow and return pipes to each of them with 15mm speedfit barrier pipe from the main 15mm flow and return pipes.

The new Valliant has been installed in the utility room immediately under bedroom 3. The gas man fitted 22mm copper pipe for the boiler up into bedroom 3 then connected to the 15mm copper pipe using 15mm PEX. Since it was installed I've noticed that while the flow down to drop 2 is hot the return is considerably colder, colder than I would expect.

My concern is that because the 22mm pipes go into 15mm pipes then back to 22mm for the drop to the living room that the pressure may not be sufficient to push the water back up the 22mm pipes for the return to the boiler.

Since we're renovating the property and it has no carpets or other flooring I wonder if it's worth me replacing the main flow and return pipes upstairs with 22mm PEX so there isn't a bottleneck. Would this be worth doing and would it be beneficial to my CH system?

While the CH warms the house we haven't managed to get it to the desired temperature yet. I had it set to 21 degrees for 6 hours today and it only reached 14. The flow temperature on the boiler never exceeded 53 even though it's set to up to 75 on the boiler. I have the weather sensor 470f which I know overrides the flow temp on the boiler but I would have expected the boiler to put more effort into warming the property. If the desired temp is 21 and temp on the thermostat says 14 then surely it should ramp up the flow temp to try increase it, that doesn't appear to happen. I'm concerned that the flow is causing the problem.

The distances are not reflected in the diagrams. The pipes upstairs are longer than they look on the diagram.

Hopefully this makes sense to everyone. I've tried not to waffle.

Existing Pipework

heating system.jpg

Proposed Pipework
proposed heating system.jpg
 
looks like your running 6 rads via 15mm pipe and that is wrong as 15mm pipe cant carry enough heat for that sort of output. you need to have the 22mm as a complete run and T off the 15 mm to the rads with a max of 3 rads of med size in 15mm. trying to keep things simple here so no heat losses etc being included

just seen 2nd pic, thats the ticket, may be better to run 22mm to the utility kitchen etc to be sure of enough heat reaching all three
 
Last edited by a moderator:
Your better off getting someone round to have a look who knows what they are doing, I could tell you the pipes are undersized but really that's probably only the start of things!
 
Agreed. I would say bottleneck is a bit rough. As suggested 22mm is a good upgrade, I would as a trial set partial load to its max 28kw? Push the chimneysweep buttons see how the house heats up?
 
Thanks for the responses.

The problem is that I had someone round, multiple people when I got the new boiler priced up. Nobody mentioned an issue with the existing pipework.

I have a 7 year warranty with the boiler so if it turns out that there is an issue with that I'll be contacting the installing engineer or Valliant. I don't live in the property yet and have access to under the floorboard so I thought it may be worth replacing the existing 15mm copper before contacting anyone.
 
If the boiler temp isn't getting above 53º the pipes are not your problem.
Look to the weather comp settings.
 
If it was a flow problem that wouldn't stop the boiler getting up to temp.
The problem with weather comp is it is not as smart as it thinks it is and neither are most of them who push it.
 
  • Like
Reactions: 2 people
So how do I override the weather comp to test getting the system up to full temp? The weather comp doesn't have very many settings to check. The boiler doesn't have any problems getting up to temp for the hot water it just seems like it doesn't want to warm up the house even though it's way off the desired temp.
 
DHW isn't controlled by comp. it's probably set to wrong curve. Firstly is the sensor on a north wall about 1.4 to 2m from floor? Is it wired or wireless?

Read the instructions it's a little confusing going frame to frame but u will get it. Installer code should still be 17. If you push two lower buttons on the boiler control panel below LCD boiler will fire into chimneys weep mode as said before? This will blast the daylight about of system. Are the rads the correct sizes for rooms? Is the house insulated? Were windows and doors closed? Did any rooms heat?
 
Yes all the radiators are sufficiently sized for each room. The BTU output exceeds the recommended for each room and all rooms have a radiator. The house has roof insulation but no wall cavity. 220mm solid brick. There are no carpets or underlay if that's likely to make a difference, also currently no internal doors.

I'll have a read through the installers manual because the operators manual didn't contain anything useful. Code on controller is still 000.

Sensor is 2m high on a north facing wall and is wireless.
 
Vaillant controls are notoriously difficult to set even for pro's who know and work these type things day in day out.
I haven't a clue how a 470 works and i have no interest in learning it. Get your installer back but if it was your idea to fit this i wouldn't hold out too much hope that he is any better educated than you on how to go through the settings.
You can probably override it short term by pressing the 2 bottom buttons. This will put it onto high fire for 15 minutes. When it cuts out press the again.
Also the bypass comes set quite far open on these. Get your installer to set it properly.
 
YThe house has roof insulation but no wall cavity. 220mm solid brick. There are no carpets or underlay if that's likely to make a difference, also currently no internal doors.

Big big difference. Weather comps come set for well insulated houses ad the curve has to be shifted to suit. Your 53º flow temp is about right for an out the box setting for an outside temp of around 10º.
 
At first glance it doesn't look too good but you have only told us half a tale, go back to the drawing and fill in all the missing bits so we don't need to take up 40 post guessing because that is what's happening, 15 mm will feed 6 radiators and I use the number 6 on the fly because it would depend on the output of each of the six, BTW you would never put 6 rads on a circuit anyway in real life, your drawing is useless without, radiator outputs and pipe lengths and diameters. I don't know the boiler set-up and I am not going to go searching, if it has and internal pump and you simply need more pump power then you may well be shot. I have repeated said this until I am blue in the face, boilers with internal pumps give you no get out of jail, the maximum pump power is fixed, you need to size the system pie work to the size of the pump, which to me as an engineer is not right.

Lets go back to that 15 mm tube, domestic system pipe work usually has water going thorough them at around 1 to 1.5 mtres per second, more than this and you will hear the water going around the system the data below might explain:

15 mm tube normal design 1 m/s will carry 0.141 ls or heat rads up to 5.9kw the pressure drop pm run will be 1000pa
15 mm tube pushed to 2 m/s will carry 0.205 ls or heat rads up to 8.7kw the pressure drop pm run will be 1600pa


22 mm tube normal design 1 m/s will carry 0.311 ls or heat rads up to 13 kw the pressure drop pm run will be 520pa
22 mm tube pushed to 2 m/s will carry 0.457 ls or heat rads up to 19kw the pressure drop pm run will be 1000pa

So you can see if you are prepared to push the envelop and you are a little deaf or have tinnitus like me you won't notice the water flow
noise. 15 mm will feed 6 rads each with a output of 8.7 divided 6 = 1.45 kw each, as I said in real life we all like an easy life if you did this it would be a pig
to balance near impossible

If you fill the as fitted drawing in properly we may be able to help, be aware of what Tamz said you need to have the boiler flow temp correct, however taking the compensation
slope out of the equation is not the answer you want.

BTW I would never design a heating system with pressure drop in excess of 500 pa per mtre run, I would go even lower to reduce pumping power and energy used in the life cycle.

PS is the pump inside the boiler case, I hate even looking for the manual, brain dead design inside the case and if it fails it will cost you twice that of one outside the case.
 
Last edited by a moderator:
I can see through their spiel you don't need the data sheet you can see it's got and internal pump
and made in Europe by our EU friends, wonder when China will start churning them out.



Vaillant ecoTEC plus - YouTube
 
Last edited by a moderator:
heating system.jpg

I've added the BTU values and pipe lengths.

I can see two problems, they may or may not be related but that's why I'm asking for advice.

The flow temp doesn't increase up to its maximum or come close. The outside temp was 1.5, room stat said 14 and desired was 21. The outside temp decreased gradually from 6 to 1.5 over 6 hours yesterday afternoon. The room temp increased from 9 to 14 over the 6 hours.

The second issue I see is that the 22mm flow pipe to drop 2 is hot but the return pipe is cold. All the other return pipes that are 15mm are not as warm as the flow pipes but are still hot.

Either these issues are both related to the boiler not getting up to temp or I have two issues and one is the flow which is why I was considering replacing the 15mm pipe with 22mm upstairs.

Thanks for the replies so far.
 
15 mm tube normal design 1 m/s will carry 0.141 ls or heat rads up to 5.9kw the pressure drop pm run will be 1000pa
15 mm tube pushed to 2 m/s will carry 0.205 ls or heat rads up to 8.7kw the pressure drop pm run will be 1600pa
If the velocity doubles then the volume doubles.

You have assumed a temperature differential of 10C. Modern condensing boilers are designed for a differential of 20C. This required a flow rate half that of a 10C differential, so a 15mm pipe can then carry twice as much heat at 20C than it can at 10C. Of course the rads have to be sized correctly taking the reduced output due to a higher differential.

A max velocity of 1 m/s is the norm for domestic systems.
 
If the velocity doubles then the volume doubles.

You have assumed a temperature differential of 10C. Modern condensing boilers are designed for a differential of 20C. This required a flow rate half that of a 10C differential, so a 15mm pipe can then carry twice as much heat at 20C than it can at 10C. Of course the rads have to be sized correctly taking the reduced output due to a higher differential.

A max velocity of 1 m/s is the norm for domestic systems.


I have not assumed anything, I have worked those figures out on DegC drop as you spotted and you are right that with 20 DegC drop the flow rates would be different, I have not assumed anything with regard to temp drop across rads just in case they have been sized for 10, the worst scenario. You need to start somewhere with novices, until now I didn't even have the rad outputs, we need to move slowly we these people too much info and they will go into overload.

Doitmyself, perhaps you could show this guy the way forward on his pipe sizing, I am sure he would appreciate it.

I can't find nothing wrong with you statement at all.

Good luck with him.
 
Last edited by a moderator:
I have not assumed anything, I have worked those figures out on DegC drop as you spotted
Then you have assumed, as the basis for you calculation, that the differential is 10C.

But that's a side issue. You haven't answered my, implied, question about flow rates.

You said:

15 mm tube normal design 1 m/s will carry 0.141 ls or heat rads up to 5.9kw the pressure drop pm run will be 1000pa
15 mm tube pushed to 2 m/s will carry 0.205 ls or heat rads up to 8.7kw the pressure drop pm run will be 1600pa

I was querying why the flow rate had only increased from 0.141 l/s to 0.205 l/s even though the velocity had doubled from 1 m/s to 2 m/s.
 
Last edited:
Then you have assumed, as the basis for you calculation, that the differential is 10C.

But that's a side issue. You haven't answered my, implied, question about flow rates.

You said:



I was querying why the flow rate had only increased from 0.141 l/s to 0.205 l/s even though the velocity had doubled from 1 m/s to 2 m/s.


take at Look:

CCI04112013_00000.jpgCCI04112013_00001.jpg
 

These are CIBSE water flow rates and you can work on the basis of constant velocity, constant pressure drop or just ignore them both and work on mass flow rate
and read off PD and still look at limiting velocity in the stepped bands. You have the best of both Words all based on water in pipe at 75 DegC, there are correction factors for different temps
but you are going to be cracking very small nut with a very large sledge hammer, doubt if that is needed on UKP
 
Doitmyslf,

Do it your way if you can help the lad, work out is PD and flow rates, he might be OK with what pipework he has installed looks to me they are all very small loads,
may have something totally wrong, and balancing by a novice is only one step down from balancing by an expert.
 
Disable the weather comp. there is a setting in the controllers installers section. Failing that put wirless compensator in freezer. This will kick boiler up the rse. Your heating should run its nuts off!
If rads still poor I would suggest that the bit of 15 needs to come out. Are the flow and returns fully open on boiler? Is your filter open and clean ( assuming you have one).

Pressure and flow rate are not proportional !

I wouldn't worry too much about the design it's an 831 31kw to hot and about 28 to heating? Pump is a good one as with boiler. Are the flue screws in the collars on boiler?
 
Disable the weather comp. there is a setting in the controllers installers section. Failing that put wirless compensator in freezer. This will kick boiler up the rse. Your heating should run its nuts off!
If rads still poor I would suggest that the bit of 15 needs to come out. Are the flow and returns fully open on boiler? Is your filter open and clean ( assuming you have one).

Pressure and flow rate are not proportional !

I wouldn't worry too much about the design it's an 831 31kw to hot and about 28 to heating? Pump is a good one as with boiler. Are the flue screws in the collars on boiler?


There you are SORTED!!! In short its just a case of tweaking it. Buxton you should be happy with that analysis, I will leave you and the experts to tweak away. Not certain which bits of 15 mm you think need to come out Ermi.
 
Last edited by a moderator:
Seems a bit off hand. It's a small domestic installation which appears to be more DIY than design. Getting all confused with flow rates and pumping head. Custard seems a bit of a techie. (Drawings and valliant wireless controls)

There isn't enough information on that drawing as previously stated, but it's a small domestic system. The problem lies with the boilers controls and setup.

The first item on his agenda should be getting the heat unit to produce heat; as everything else is conjecture and misleading.

Once the boiler is returning hot water then look at system design. The boiler would reach max temp with two 600 450 p+ rads fed on 8mm and returned on 28mm if the comp was set up properly!

The bit of 15 I was referring to was the concentric bit 22 - 15 - 22 .

The installer ???? Is out of the picture by sounds of it , so better focus on the op. ( installer??)
 
The bickering is amusing and rather familiar, I see the same thing on a Tech forum that's in my area of expertise.

Thanks all for the help. I believe I have something to work with now.

The guy that installed the boiler and controller didn't really know much about the WC so the defaults were left in place. The heat curve was left at 1.2 so I will increase that to push the flow temp up and see what that does.

I still think that while I have easy access to under the floorboards it may be worth changing the main flow and return pipes to 22mm but I will leave that to see the impact of increasing the flow temp.

After I get the flow temp up I'll check that the rads are getting warm enough and whether the flow and return from drop 2 are both warm. I was concerned that because the drop uses 22mm pipes the 15mm pipes upstairs wouldn't have enough flow to push the returning water back up.

The original installer isn't out of the picture he just doesn't really know anything about the WC. I thought it would be a good idea to get some opinions before changing the pipes which I can do myself. No point getting someone in to replace two lengths of 15mm pipe with 22mm when I could do. I'm sure everyone on here does things themselves that they could get someone else in to do, does that mean it's done any worse than if you paid a professional?
 
  • Like
Reactions: 2 people
Buxton,

You are more observant than most, but bickering it isn't, its not even a difference of opinion, but you are smart enough to work out what it really is, this last line of your post is 100% spot on.

"I'm sure everyone on here does things themselves that they could get someone else in to do, does that mean it's done any worse than if you paid a professional?"

I wish you well with your endeavours, I would not blame you if you did not come back and tell us how you went on.

Tony
 
Last edited by a moderator:
I suggest you take a look at the same table. The flow rate of 0.205 l/s is for a velocity of 1.5 m/s not 1.0 m/s. The table does not show the flow rate through a 15mm pipe at 2 m/s.

Flow Table.jpg
 
I suggest you take a look at the same table. The flow rate of 0.205 l/s is for a velocity of 1.5 m/s not 1.0 m/s. The table does not show the flow rate through a 15mm pipe at 2 m/s.

View attachment 15751


How right you are, me at 5 am must stop posting at that time, nice one, nice colouring in too, colour scanner, woow, and like I said you won't find me designing down the bottom of the page at those high velocities, 0.5 to 0.75 is fast enough
 
Last edited by a moderator:
I replaced all the radiators with bigger doubles and installed some new ones in rooms that didn't have them.
According to the data you provided later, you now have 9.6kW of rads (BTU are no longer used).

Do you know what your actual requirements are? If not, use the Whole House Boiler Size Calculator, but set the Domestic Hot Water Allowance to 0. This will give you the central heating requirement, which I would like you to post.

While the CH warms the house we haven't managed to get it to the desired temperature yet. I had it set to 21 degrees for 6 hours today and it only reached 14. The flow temperature on the boiler never exceeded 53 even though it's set to up to 75 on the boiler. I have the weather sensor 470f which I know overrides the flow temp on the boiler but I would have expected the boiler to put more effort into warming the property. If the desired temp is 21 and temp on the thermostat says 14 then surely it should ramp up the flow temp to try increase it, that doesn't appear to happen. I'm concerned that the flow is causing the problem.
I suspect that the reason for the house not heating up properly is that the boiler is cycling due to it being oversized compared to the total rad output.

You have 9.6kW of rads fed from a boiler which can produce between 5.5 and 25kW. It is starting off at max output, but is unable to modulate down fast enough, so the water temperature rises very quickly and the boiler has to cut out and cool down. The average temperature is therefore much less than expected, so the rad output is less.

The solution is to restrict the max output of the boiler to say 12kW

As for pipe sizes, it all depends on what temperature differential you use. The boiler expects a 20C differential, so you should really be balancing the rads at 20C. The result from the boiler calculator (link above), when compared to the total rad output, will tell you if this is possible. The rad total need to be at least 20% greater than the heating requirement to allow a 20C differential.

If this is possible, there is no real need to change any of your pipes.
 
Hi all. Thanks for the responses.

I've managed to get it sorted by implementing a number of things people have mentioned.

1. I did a chimney sweep and got the flow up to 75 degrees, did it twice so it ran for 30 minutes. I still had the same issue with the 22mm drop 2 pipes. Flow pipe was too hot to touch, return was just better than cold.

2. Increase heating curve to 4 which sorted the flow temp, reduced back to 2.4 after I did the below things as 4 was too excessive. It was set to 1.2 originally.

3. Fully closed all lockshields for upstairs radiators then gave them a 1/4 turn on. Someone I had read about else where. Still had the same problem with 22mm drop 2 pipes although the return was now hotter and the rads got warmer than before.

4. Drained the system, replaced the main flow and return with 22mm pipe. Feeding each individual rad with 15mm pipes. Added an additional rad on the landing upstairs and a second rad in the dining room which comes off drop 2. Added inhibitor through my towel rad and refilled the system.

The house now gets up to temp despite having poor insulation due to the other refurbishment work I'm performing. The flow and return to drop 2 seems to be much closer in temp, no longer have a cold return pipe.

I have the night temp set to 12 degrees which it maintains with the flow temp of around 25-28. This is probably a little higher than it will be when the house is finished because I still have 14mm underlay and carpets to lay, external door frames to seal and insulate, two 4 inch extractor fan holes to insert extractors and mortar, open chimney from where the back boiler was etc...

All in cost me an additional £54 for 22mm pipe, £40 for fittings and £400 for two additional rads plus 6 hours of my time yesterday. The missus insisted on having a designer horizontal rad for the landing hence the expense on the rads.

Thanks for the help

Chris
 
  • Like
Reactions: 1 person
Chris,

I had an idea that you would not let go and you would fix it yourself, well done and well thought out, I never thought you would do it by just tweaking or the boiler was oversize

Nice you came back after all!!!

Now get the house airtight
 