Pauld1962

DiddlyP
Hi .. I am GSR ... Been doing combi repairs mainly and swaps.. I've been asked to remove old gravity system and install combi ... My thoughts would be to drain everything down removing all old tanks and cap off all in airing cupboard... Then route flow and return under landing floorboards to new boiler location in kitchen ... All other services are available there.. My question is ....am I missing something regarding the capping off and flow/return ...

Many thanks ..... Diddy
 
Hi Scott...Sorry don't have any pics ...its a very old system ...no valves just a pump and microbore pipework to rads... There is is some 15mm stuff so work has been done at some point .. Cheers

Diddy
 
this is an honest opinion i would re pipe the lot, chances are the 10mm is going to be nearly blocked with crud / going to give you problems when you flush the system
 
I considered that but the customer isn't too happy with the disruption, concrete floors throughout ..!! She does have paperwork from BG regarding Powerflush 2 years ago ...
 
I considered that but the customer isn't too happy with the disruption, concrete floors throughout ..!! She does have paperwork from BG regarding Powerflush 2 years ago .

any pipework in the concrete floors? and tbh that doesnt mean toffee
 
One gravity to combi conversion I did ended up with new drops to a couple of rooms anyway due to higher pressure disrupting pipework under concrete floor / making them a lot more noticeable, losing pressure etc.
 
Beware paul chances of this being 100 per cent successful is very small i would recommend you repipe it all on a drop type system abandon the pipework in the concrete floors , cover yourself by explaining to the customer that this may work out and your reasons why ie you are pressuring old pipework not a good idea , debris in there even after a BG powerflush ha ha chances that was done properly is very small , if it gonna be done do it right otherwise it will bite you . cheers kop
 
If you not sure how to go about converting a old gravity system get someone to help you (older plumber) as you can come unstuck, not always as straight forward as you think, Better to do a re-pipe , if system is working give it a good run to make sure that all rads are getting hot, if not & customer doesn't want a re-pipe ! walk away .
 
Hi ... Thanks for all the input much appreciated... I called at the customers yesterday and tested the heating as JTS suggested.. All rads get hot within 10 mins... I'm not doing the job for a couple of weeks now so will let you know how I get on ... I think I will be draining down and capping everything off in airing cupboard, then tap into flow and return on heating under the landing floor .. Thanks ... Diddy
 
I have never done one but I didnt think you could flush microbore .. anybody ?

Have tried to flush a microbore system once. It worked for 6 months then got blocked up again. Customer was most unhappy even though I explained before hand that it probably wouldn't work for any length of time. I tried to explain that the smaller bore means you don't get enough flow through the pipework to dislodge everything.

Compare this to 15mm where every system has worked a treat afterwards and we've had no complaints.

Wouldn't do a microbore system again.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "New to the buisness ... Info required." which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
Pauld1962,
Last reply from
Scott_D,
Replies
19
Views
2,715
Back
Top