First post here just looking for help or a link to setting up an oil fired condensing boiler. What is the ideal temperature for flow and return,is it 70/50, 75/55 and also what should the drop across the rads be? Should it be 12c or 20c. Thanks for any help
 
Grant boilers are set at 70deg flow and the aim is to achieve a 50deg return, the boiler will then condense
 
I believe both grant and worcester state a minimum return temp of 40deg C to prevent condensate forming in the mild steel primary HEX not normaly a proble with rads though.
 
It's a warmflow 90 greenpak with a riello burner. Thanks for help. Should the rads be balanced differently ie with 20c drop instead of 12c?
 